Adiabatic equation and bonding | Page 2 | on ElectriciansForums
Discuss Adiabatic equation and bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
if the 6mm main bonding shows no sign of deterioration and is proved to be connected and intact, then there is no requirement to change it. (TN-S)
so 6mm tn-s c
10mm tn-c-s
6mm tt
tn-s and tt can be smaller bu ysing adiabiatic what reg number gary m.. to finish me off , got book right here.. thaxnks
Can somebody have a look at this and tell me which tree I'm barking up?
Using the Adiabatic equation to determine the required size of main bonding and therefore the size of supplementary bonding.
Ze = 0.18
PFC = 1.3 kA
Fuse type 1361 IIa
S = square root (1300 x 1300 x 0.1) /115
= 3.57
Is that right? Seems like a very low value for main earth
No nearly, but not quite.
Should be: S = √(1100 x 1100 x 0.1) / 115
= 3.03.
For a BS1361 80A fuse:- from Table 54.2 k=143 and from Appendix 3, fig3.1 1100A @0.1s
S=√(1100[SUP]2[/SUP]x0.1)/143
S=2.43mm[SUP]2[/SUP]
Good thread on the adibiatic guys. Would any of you know if actually fitting a main earthing conductor on a TT or TN-S is notifiable or not?
Cheers
His wording isnt clear but he mentioned main earth at the bottom of his equation so his intention was selecting the size of bonding conductors in accordance with the calculated size of his earthing conductor.
Widdler is absolutely correct in what he stated, according to what the OP had posted!!
The adiabatic equation is used for sizing of the earth conductor and protective conductors only, It's ''NOT'' to be used for bonding conductors.
Reply to Adiabatic equation and bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net