What's the earthing arrangements of the supply? Hopefully not PME?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Adiabatic equation and bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
No nearly, but not quite.Can somebody have a look at this and tell me which tree I'm barking up?
Using the Adiabatic equation to determine the required size of main bonding and therefore the size of supplementary bonding.
Ze = 0.18
PFC = 1.3 kA
Fuse type 1361 IIa
S = square root (1300 x 1300 x 0.1) /115
= 3.57
Is that right? Seems like a very low value for main earth
Would any of you know if actually fitting a main earthing conductor on a TT or TN-S is notifiable or not?
Cheers
His wording isnt clear but he mentioned main earth at the bottom of his equation so his intention was selecting the size of bonding conductors in accordance with the calculated size of his earthing conductor.
Using the Adiabatic equation to determine the required size of main bonding and therefore the size of supplementary bonding.