So I'm looking into the thermal constraints of every cable in my 2396 project.

I've used the adiabatic equation in a spread sheet and 99% of them are fine with the CPC I have selected.

However, there are a few really short circuits with very low earth fault loop impedance. Because of this the prospective fault current is really high and the adiabatic equation says I need a larger CPC.

Not a problem, I enter the adjusted values for the larger CPC into the spread sheet which automatically does the equation again....

Now because I've used a larger CPC, the loop impedance is even lower and the prospective fault current is even higher. It now says I need a larger CPC (again).

This seems to be an infinite loop.

Please can someone explain how I get around this?

Thanks
 
Quick thought - have you included a practical value for Ze in your calculator? The Ze will not be zero and you aren't making it any smaller, so it should converge ... he says hopefully :)
 
I think I will have to change cable type and use the minimum size conductor like Strima said.
 
If your using 0.1 seconds as T for say mcbs then there’s your problem if your disconnection time is below 0.1 seconds.
Get the let through energy from the manufacturer.
You’ll need to make sure k2S2 is equal to or greater than let through energy of the OCPD and using t=k2S2/i2 you’ll probably see that if your cable sizes comply, t being the maximum time before damage to the conductors and surrounding insulation starts to occur then your circuits will Probably comply.
 
Can you give an example that won't work for you ?

So the Zs is 0.2315764 ohms (3 metre circuit using 1mm/1mm singles).

Cmin Ă—nominal voltage = 218.5.

218.5 / 0.2315764 = 943.5331061 amps.

Looking at the curve for 6A type C 60898 on page 326 in the BYB it has to be 0.1s disconnection time.

Therefore the square route of 943.5331061 squared timed 0.1 = 298.3713663.

298.3713663 divided by my k value of 115 = 2.59mm minimum CPC required.

Like I said if I go up a size then use the equation again I will have go another size and so on and so on.

I guess I could have the wiring go round the room a couple of times to increase the Zs value therefore lowering the fault current :confused:
 
Yes as stated you need to find out the let through of the protective devices(the units aren't energy it's more like energy per ohm)
You would have an mcb with a bs fuse upstream so for higher pfc the fuse would blow first. Although with a normal sized lv transformer you would only get a maximum of 10kA or so? even if you were connected directly to the transformer due to the volt drop inside the transformer.
Also bear in mind the cpc size of the final circuit wouldn't affect the fault current because you're considering the case where the fault occurs directly after the mcb (ie worst case) so you would use zdb not zs.
For all other calculations eg disconnection time and volt drop the worst case is the far end of the circuit, but not for adiabatic.
Hope that helps!
 
So the Zs is 0.2315764 ohms (3 metre circuit using 1mm/1mm singles).

Cmin Ă—nominal voltage = 218.5.

218.5 / 0.2315764 = 943.5331061 amps.

Looking at the curve for 6A type C 60898 on page 326 in the BYB it has to be 0.1s disconnection time.

Therefore the square route of 943.5331061 squared timed 0.1 = 298.3713663.

298.3713663 divided by my k value of 115 = 2.59mm minimum CPC required.

Like I said if I go up a size then use the equation again I will have go another size and so on and so on.

I guess I could have the wiring go round the room a couple of times to increase the Zs value therefore lowering the fault current :confused:
Yes but your disconnection time will be less than 0.1 seconds ,you need the let through energy of the device from the manufacturer.
Also use the thermal constraints calculation I’ve already stated above.
Do not use 0.1 seconds.
Also your mcbs will be current limiting class 3 devices, you shouldn’t have an issue
 
Hi - in practice would you have a 1mm circuit that is only 3m long? Anyway, if pssc was 1000A and we use 100ms disconnect time then I2T is 100k. Looking at the Wylex B6 graph, it shows about 2k let through energy for 1kA which will give a very different result :) .

[ElectriciansForums.net] Adiabatic equation infinite loop
 

Reply to Adiabatic equation infinite loop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
725

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
  • Question
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
Replies
7
Views
608

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top