Just realised from wilkos post even that's wrong, it should not be calculated from the zdb, it should be the PFC which would be the maximum of the PSSC and the PEFC.Also bear in mind the cpc size of the final circuit wouldn't affect the fault current because you're considering the case where the fault occurs directly after the mcb (ie worst case) so you would use zdb not zs
But still the final circuit would have nothing to do with the let through (energy per ohm)