Is it acceptable to use the adiabatic equation to work out the size Main Earthing conductor to install in a standard domestic property for a consumer unit change.

Ive always been under the impression that its 25mm tails and 16mm main earth for a tns or tncs system, but a colleague thinks its acceptable to install a much smaller main earth as long as its ok by the equation.

Any help very much appreciated.
 
why bother with equations when it's so simple to bung in a couple of ft. of 16mm.
 
if you assume a TN-S with a Ze value of 0.8, then your pefc would be 300A assuming 240v. that's the minimum fault current flowing through that earth conductor. could be considerably more if Ze is ( as it usually is ) lower. that's why we all use 16mm.
 
Hi

Is it acceptable to use the adiabatic equation to work out the size Main Earthing conductor to install in a standard domestic property for a consumer unit change.

Ive always been under the impression that its 25mm tails and 16mm main earth for a tns or tncs system, but a colleague thinks its acceptable to install a much smaller main earth as long as its ok by the equation.

Any help very much appreciated.

Your colleague is correct. It can be obtained by calculation or measurement.
 
true, problem is, if say, by using the adiabatic equation, you quite correctly chose to use , say, 10mm, then along comes mr. clipboard ans says " that's no good, it's got to be 16mm." sometimes you just can't win.
 
true, problem is, if say, by using the adiabatic equation, you quite correctly chose to use , say, 10mm, then along comes mr. clipboard ans says " that's no good, it's got to be 16mm." sometimes you just can't win.

I can't argue with that. Happened a few times to me before, I took a white board to a building site once, embarrassed the hell out of him.
 
Don't forget Table 4.1 in the OSG

Page 28

A PME install requires 16mm Earthing conductor even with 16mm Tails
 
Last edited:
Whole estates of 100's of houses built in the 90's onwards by reputable national buiilders under a NHBC buildmark have 10mm earthing conductors on 60A 1361 type 2's service heads marked with a pme label. Someone within their design teams must hold a firm belief that this is appropriate. I guess though that this will be discussed for ever more withopinion polarised and that I will be confused for evermore..
 
The Adiadatic equation should only be used for CPC calculations only. The BGB gives guidance on main earthing conductors and bonding conductor sizes that should always be followed.

Beware that this equation is only a small part of a cable calculation. If used incorrectly you may find that R1+R2 and Zs readings may be excessive.
 

Reply to Adiabatic Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes. Things...
Replies
5
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top