Whole estates of 100's of houses built in the 90's onwards by reputable national buiilders under a NHBC buildmark have 10mm earthing conductors on 60A 1361 type 2's service heads marked with a pme label. Someone within their design teams must hold a firm belief that this is appropriate. I guess though that this will be discussed for ever more withopinion polarised and that I will be confused for evermore..

Maybe since then some of those houses have burnt down and they've had to reconsider?
 
I'm 99% sure that using the adiabatic equation on all types of 100A BS 88/1361s, the results given require only a 10mm earthing conductor to be used for any of them, hence why I very rarely fit 16mm earthing conductors for domestic work. I have a couple of 100m rolls of 10mm in my van at all times for bonding, I'm not gonna spend the extra money on anything larger than 10mm unless I have to.
 
I tend to use 16mm just because it's easier and I'd rather go too big than too small. I suppose it could be classed as laziness.
Purely out of interest, and I'm not having a pop at ya, what's easier about using 16mm as opposed to 10mm? Personally, I find 10mm a whole loit easier to navigate around a CU.
 
Purely out of interest, and I'm not having a pop at ya, what's easier about using 16mm as opposed to 10mm? Personally, I find 10mm a whole loit easier to navigate around a CU.

You're absolutely correct, of course. I do indeed use 10mm. Don't know what I was thinking. :rolleyes4::rolleyes4::rolleyes4::rolleyes4::rolleyes4:
 

Reply to Adiabatic Equation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes. Things...
Replies
5
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top