Hi Folks,

If I'm extending a lighting circuit, (adding two pendants and an outside light) from an existing pendant but the board doesn't have any protection (an old BS3036 fuse board) What's the best way to add RCD protection?

The new cable for the switches can't buried more tore than 50mm deep and I don't want to whack an RCD FCU anywhere as they are quite bulky.

What would be the best course of action to take to install this circuit so it complies with the Regs?

Thanks,
T
 
You could install a 3 module consumer unit fed from your 3036 board, then install an RCD and 6a mcb for the lighting circuit in this cu, which is notifiable work.

But, by the time you’ve gone to all that effort for just 1 circuit, you’d be better off upgrading the complete board and protecting the whole house.
 
You could install a 3 module consumer unit fed from your 3036 board, then install an RCD and 6a mcb for the lighting circuit in this cu, which is notifiable work.

But, by the time you’ve gone to all that effort for just 1 circuit, you’d be better off upgrading the complete board and protecting the whole house.
If done SpinLondon,s way would it still be notifiable? the OCPD at the origin of the circuit would be unchanged, only addition of additional protection.
 
I figured the RCD FCU at the origin would be the simplest solution.

As the old Wylex Fuses for lifting circuits are rated at 5a... What size fuse would I put in the RCD FCU? A 3a?

I believe there are currently 4 pendants on the circuit.

I don't think it would be notifiable because i would just be adding a fuse on the existing wiring, it just happens to be next to/near the fuse board?

Correct me if I'm wrong.
 
As the old Wylex Fuses for lifting circuits are rated at 5a... What size fuse would I put in the RCD FCU? A 3a?
You need to get your discrimination tables out to answer that one!
My gut feel is that it won't discriminate.

But, whoa fella. Why an RCD FCU?. Just install an RCD.
You do not need any additional fusing.
 
Last edited:
I would say the fuse is largely irrelevant as it is not needed to provide protection, the fuse in the DB is doing that.

All yo really want is an RCD.

Slap a 13A in it.

If such a beast existed, you could fit a non fused RCD spur.

Tin hat on.
 

Reply to Advice on Installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
541
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes. Things...
Replies
5
Views
439
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top