Hello people
Got job to replace/move cu going to be using 25mm 3 core swa as tails as ive never used swa as tails before im after a bit of advice. Do i earth armour of cable at supply end using a 16mm fly lead to gland. As im using the 3 core 25mm how do you terminate the earth in the cu earth terminal as all domestic cu ive seen only accept max of 16mm. One more question the customer has asked me to quote to install two showers one in main bathroom one in en-suite i thought two electric showers in one property was not good practice as could lead to over load problems if used at same time, with going down the route of installing equipment to allow only one to run at a time, time just wondered what others opinion on this was. Dont want to lose work, as i know some will fit without a care , advice please.
Ta
neil
 
Bes...i`v had to do this before....when i had to take a feed from the meterbox to a C/U in a kitchen using an armoured clipped direct to an outside wall...and into the kitchen that way....
if its gettin it into the meterbox....you could cut a bit of the wall away at the edge of the meterbox.....to allow the SWA to get into the meterbox.....kind of fly it in like...
 
I would use 2 core SWA (25mm) and use the Steal armor as the Main Earth at each end terminate into a metal clad box and come from there with a 16mm earth to the CU (one end) and DNO supply (on other end). If using 3 core SWA (25mm) then run the 3rd wire as the earth and terminate that into the box as well as an additional earth to the Steal Armour. Either way the Steal Armour needs to be earthed.
 

Reply to Advice on swa as tails in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
823
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
906

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top