I had a interesting experience this week with an EICR in a commercial unit. All units are 3 phase some are PME others TT with rods out front in chambers. all units have structural steel which is bonded. water pipes inside is bonded but incoming pipe is blue plastic. a properr ra with wander lead connected to rod gave 27 Ohms.. with all things connected i got a 'zsdb' of 0.24
Out of curiosity I took the wander lead round to adjacent units, just about reached the cutout in one. it seems the units being joined through steel work, reinforced foundations and metal in the roofs etc have created one large linked system. it is debateable then whether the unit i tested is still TT as it has a link through structural steel to the PME cut outs. all utilities are via plastic pipes so the only shared paths are are the steel in the buildings. makes for an interesting fault current path.