The origin is TT with a SWA supply 63 amps 100 ma S type RCD to house. House is 30 metres away through 2 x farm type barns.
I have installed a new earth rod for the house, so my question is should I leave the earth connection to SWA armour at the house or only earth the SWA at the origin supply end and rely entirely on the new earth rod for house earth. Ze for earth rod is 85 ohms so pretty good. Zs at house board (inc armour and bonding) is 17 ohms.

Thanks in advance.
Steve.
 
If I'm reading this properly, you've now got (or would have) an earth rod at each ends of the armour supplying the house, yes? As far as I can see, so much the better as you've just reduced your Ze figure a bit more. It's no different than hammering in two rods in one place to achieve the same.
 
If I'm reading this properly, you've now got (or would have) an earth rod at each ends of the armour supplying the house, yes? As far as I can see, so much the better as you've just reduced your Ze figure a bit more. It's no different than hammering in two rods in one place to achieve the same.

This should of course actually be your Zdb figures, reflected in your Zs measurements, and assumes that you've properly banjo'd both ends into something which is also eventually via various routes bonded back to the MET. Hence why a measured Zs is almost never ever exactly Ze+(R1,R2) due to parallel earth paths.
 
Last edited:

Reply to Advice please guys. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top