Hi Just wondering if anyone can help me out. Is it possible to get 0.03 to 0.09 m amps on a clamp meter on copper water pipes when an appliance is plugged in and the unit attaches to hot water copper pipes via a metal braided hose? On 2 x units the first unit had external damage with messed up electronics. This was replaced. Then a second unit shows the same fault with electronics which runs off low voltage 12v (main unit runs on 230v). When you unplug the unit from the socket the m amp go to 0 on copper pipes and it is a intermittent fault.
Is it possible that maybe its from the neutral side of a socket leaking to earth somehow and when the unit is plugged in and feeds the neutral it rubs on to the earth some where? I can't prove it and it does not trip the rcd.
The earth pin of plug to chassis gives continuity under 0.1 ohm.
The copper pipes to socket screw gives continuity 0.39 to 0.98 ohm on cold and hot pipes.
The socket and see loop tester gives under 1 ohm; 3 green dots.
Insulation test 999 on live and neutral to earth on unit.
Tried using volt meter; neutral to pipes 0 volts and on 0.0 to 0.00 setting reading got few low numbers but got them before I even touched the copper pipe and no way to reset to 0 on volt meter. Therefore inconclusive if any volts on pipework. Going back with a third unit as client says electrician has checked electrics and believes it is the units. I can't see two units having the exact same fault. Would appreciate any advice / thoughts. Thanks.
Is it possible that maybe its from the neutral side of a socket leaking to earth somehow and when the unit is plugged in and feeds the neutral it rubs on to the earth some where? I can't prove it and it does not trip the rcd.
The earth pin of plug to chassis gives continuity under 0.1 ohm.
The copper pipes to socket screw gives continuity 0.39 to 0.98 ohm on cold and hot pipes.
The socket and see loop tester gives under 1 ohm; 3 green dots.
Insulation test 999 on live and neutral to earth on unit.
Tried using volt meter; neutral to pipes 0 volts and on 0.0 to 0.00 setting reading got few low numbers but got them before I even touched the copper pipe and no way to reset to 0 on volt meter. Therefore inconclusive if any volts on pipework. Going back with a third unit as client says electrician has checked electrics and believes it is the units. I can't see two units having the exact same fault. Would appreciate any advice / thoughts. Thanks.