A customer recently lost power to part of their electrical installation. On arrival I found all IEC 60947-3 devices had supposedly tripped - including the main switch rated at In 400A. Excluding the possibility of someone tapering with the board, can anyone think of any other reason why this may have occurred?
 
It seems the OP isn't paying heed to your question.
Sure looks that way,

[ElectriciansForums.net] All devices on 3phase board tripped simultaneously


I wonder if the O.P remade the 400a Mainswitch and survived and or all the other tripped devices?
 
Some
Leaving the main switch aside, unless something simultaneously affected every single distribution circuit between this board in question and the downstream boards, it surely has to be manual operation.

What sort of cables are feeding the downstream boards, are they mechanically protected?
I have once found several circuits all chafed on poorly installed metal trunking which then got hit causing it to cut into all of them.
I think I'd IR a couple of the distribution circuits, rule out cable damage, and declare that the only logical reason is manual operatiomajority of the of the cables are SWA properly glanded into the top of the board.
Leaving the main switch aside, unless something simultaneously affected every single distribution circuit between this board in question and the downstream boards, it surely has to be manual operation.

What sort of cables are feeding the downstream boards, are they mechanically protected?
I have once found several circuits all chafed on poorly installed metal trunking which then got hit causing it to cut into all of them.
I think I'd IR a couple of the distribution circuits, rule out cable damage, and declare that the only logical reason is manual operation.
The majority of cables are SWA properly glanded into the top of the board and going off in different directions to different parts of the building.
[ElectriciansForums.net] All devices on 3phase board tripped simultaneously
 
Last edited by a moderator:
I thought a 60747-3 could incorporate overcurrent protection and that the In was the devices rating. Please forgive my ignorance if this assumption is wrong.
No if it incorporated trip functions it would be 60947-2 and also with a device of that size it can be adjusted, I assume it doesn't have these features.
What is the part no to be doubly sure.
 
That appears to be a Hager H301E which is a switch 'disconnector Isolator'. In which case it does say IEC 60947-3 on the front.
It has a "push to trip" button, but I think that is a mechanical trip for turning off the switch, not current operated.
In which case the only way it will switch 'off' is someone operating it.
Can anyone confirm?
 
Couldn't swear to the H or the 1, but I'd be inclined to go with HC301E, which Hager designate as 'non auto'.

Beyond my experience, but here's a link to some data from Hager. Page 3.30 gives a limited amount of information, but does state BS EN 60947-2 on the table in which this is included. Despite this, every image I can find of this isolator does indeed state 60947-3.

Clear as mud.
 
It’s a care home. The board is not readily accessible, but not impossible to get to by any of the staff. Please see a close up of main switch - I’d love to determine whether this is a manual isolator only.
[ElectriciansForums.net] All devices on 3phase board tripped simultaneously
 
Last edited by a moderator:

Reply to All devices on 3phase board tripped simultaneously in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
877

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top