Steve T

-
DIY
Joined
Apr 6, 2017
Messages
221
Reaction score
130
Location
Newcastle
Hi all,
I'm helping a friend of mine do up an old cottage that he has bought recently. Most rooms are in such a state that they need completely redoing. Our first project was to rip out one of the bathrooms, and in doing so we had to disconnect an old infrared wall heater, where we discovered aluminium t&e. It's definitely PVC not rubber. I had a quick look in the ceiling rose in that bathroom and it also appears to be wired in aluminium t&e. We didn't look at anything else today so I don't know what other circuits may or may not have aluminium t&e.

The property has clearly had quite extensive electrical work over the years(has had an extension and loft conversion) as well as some diy bodges, as I suppose is to be expected. The CU is also not original, it looks like it should be a 16th edition split load but someone has replaced the main switch with an RCD. So clearly the CU has been changed at some point.

I'm definitely going to suggest he gets an EICR done, but do you think the aluminium t&e presents an immediate problem and should be rewired, or is it still OK to be in service?

Also if we have to work with the aluminium t&e at all (changing lights, sockets etc) how should we treat it? It's all stranded of course, so should we use ferrules on the ends and connect to screw terminals directly or into wagos and 'pigtails' in copper to the accessory?

I haven't got any pictures at the moment unfortunately but I am back at his house tomorrow so I can get some (of the CU, and anything else?)

Thanks!
 
I've come across very little aluminium t&e seen more alcumic and all aluminium mic and what a disaster that stuff was
EDIT just remembered had to terminate a large aluminium swa with double crimped lugs many years ago not something I'd want to repeat
 
Back in the depths of time my father used some aluminium cable when there was a copper shortage, and I have seen some but it was solid conductors not stranded.
BT (or it was probably Post Office Telephones back then) went through a phase of using aluminium when copper was in shortage. It created decades of problems for them as the slightest water ingress turns aluminium cable into a plastic tube full of white powder.
Back in the 90s/00s, where I worked we had a site on the Isle of Wight and fell victim to this. In total we had about 9 pairs into the building, and no end of faults. Eventually BT ripped out the old ally cable (a trunk cable somewhere between the exchange and our site) causing all the faults, so while the site was completely offline for a few hours, we had no faults after that.

Still, dad had a tale of using silver for busbars during the war. He said they kept meticulous records of where, and it was all replaced with copper when it was available.
 
BT (or it was probably Post Office Telephones back then) went through a phase of using aluminium when copper was in shortage. It created decades of problems for them as the slightest water ingress turns aluminium cable into a plastic tube full of white powder.
Back in the 90s/00s, where I worked we had a site on the Isle of Wight and fell victim to this. In total we had about 9 pairs into the building, and no end of faults. Eventually BT ripped out the old ally cable (a trunk cable somewhere between the exchange and our site) causing all the faults, so while the site was completely offline for a few hours, we had no faults after that.

Still, dad had a tale of using silver for busbars during the war. He said they kept meticulous records of where, and it was all replaced with copper when it was available.

Some estates round here have the same problem with ally BT cables. Built late 70s/early 80s roughly.
 
Update: so I went back and took a bit of the cable home with me. Here are some pictures:
[ElectriciansForums.net] Aluminium wiring

As the pic shows the CPC is solid and both L&N are 3 strands.
[ElectriciansForums.net] Aluminium wiring

I scraped at the wire with a knife and copper was revealed underneath the silver surface, so as lots of people suggested it appears to be tinned copper PVC t&e.
Thanks all for your help
 
Most of the BT aluminium cable was installed in the mid to late 70's and most of the houses round where I live were built from about early 74 up to 78 / 79 and nearly all the trunk cabling into the area is aluminium, when they first introduced ADSL there were loads of problems getting anywhere near the speeds they claimed and a lot of it was down to the aluminium
 
Most of the BT aluminium cable was installed in the mid to late 70's and most of the houses round where I live were built from about early 74 up to 78 / 79 and nearly all the trunk cabling into the area is aluminium, when they first introduced ADSL there were loads of problems getting anywhere near the speeds they claimed and a lot of it was down to the aluminium
I thought BT tried to introduce ISDN first before ADSL.....

My uni lecturer called it “It Still Does Nothing”
 
I thought BT tried to introduce ISDN first before ADSL.....

My uni lecturer called it “It Still Does Nothing”
Indeed they did. And back in a time when I tried to escape from electrical work I had two 'banded' ISDN lines into my house, giving me a blistering..... 256K
 
Alternatively, ISDN stood for I Smell Dollars Now
Another of those BT policies. In principle, it should have been a good option to nudge people towards ISDN - especially if they'd used the NTEs with built in analogue adapters. They could have had people on "digital to the premises", and with some additional diagnostics via the digital link. And for people wanting two lines (e.g. phone and fax - remember those ?), only one pair.
But no, they didn't want to risk damaging their leased lines cash cow - so ISDN was priced to avoid that risk, and it never really became a "mass" product.
They did the same thing with ADSL at first - deliberately priced to stop people ditching their leased lines. I recall back in the 90s we had two 64k leased lines - about 6k/year each IIRC. These days (or rather, at my last job) we just put in ADSL and run a VPN for something like 1/10 of the cost and higher bandwidth.
 
Still, dad had a tale of using silver for busbars during the war. He said they kept meticulous records of where, and it was all replaced with copper when it was available.
I seem to remember a story about when they were making the atomic bombs for Hiroshima etc... they needed to make large electro-magnets, for which you'd usually use copper of course. However it was wartime... copper was very scarce, but they had large reserves of silver in the state vaults... so they used that instead. Then after they'd finished with it... it was smelted back into ingots ! Perfect recycling !
 
They did the same thing with ADSL at first - deliberately priced to stop people ditching their leased lines. I recall back in the 90s we had two 64k leased lines - about 6k/year each IIRC. These days (or rather, at my last job) we just put in ADSL and run a VPN for something like 1/10 of the cost and higher bandwidth.
I remember working for a Telco years ago when SDSL was just starting... we had a bunch of demo connections for sales purposes... and the speed increase was dramatic ! It was almost like science fiction to us...
 

Reply to Aluminium wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

The MCBs are branded Noark.
    • Like
Replies
5
Views
360
thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
314

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top