On a distribution board last week in a farm house, I saw 2 core 4mm SWA with the sheath terminated by having a couple of strands in a terminal block.

A photo would save a thousand words, but I found out on that day that my camera phone is not waterproof =-(

The other sparky on site said it is fine if the Zs is in, which I accepted at the time.

Then I got thinking, the Zs will make sure the fuse trips, but how can you guarantee conductor safety while the fuse is tripping?
We had a similar issue in our factory where a spark proved that a distribution circuit would blow in 4s, within the limit. However I pointed out the wires would be melting the insulation after 1s.

I can do the calcs to prove how hot that conductor will get, but that is not sparky level maths and I know the guy who installed it won't be able to do that.

So my question is:

When is it ever safe to terminate only a couple of strands of the armouring on SWA when it is being used as the CPC.

This is quite important as I am going to be politely confronting the guy, and I don't want to risk causing offence if I am wrong. I will be the first to admit domestic is not my speciality.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Am I being a snob, or is this actually dangerous
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
135
Unsolved
--

Advert

Thread statistics

Created
Inteificio,
Last reply from
QSGAZ,
Replies
135
Views
12,973

Advert

Back
Top