Got a call from a mate today. All power out. Seems cutout fuse blown, they just had a new hot tub put in.
Opened meter box to find this. I think it's complete arse on many levels, but DNO chap came out and replaced fuse without any whinging. I was quite surprised, but I guess it's a Sunday!
 
5 4 3 2 1....

[ElectriciansForums.net] Am I being over picky or is this just rough?
 
An SWA with no gland, single insulated and unprotected conductors going straight to the block, doesn't look like the SWA is earthed? I assume the grey tails are feeding the original CU in the house. What is in the capping to the right?
In my opinion the SWA should be discon from the block asap.
 
An SWA with no gland, single insulated and unprotected conductors going straight to the block, doesn't look like the SWA is earthed? I assume the grey tails are feeding the original CU in the house. What is in the capping to the right?
In my opinion the SWA should be discon from the block asap.

Spot on,
looks like armour is not bonded.
Because the single insulated conductors are in an enclosure requiring a tool or key to open I think they are ok being single insulated.

I would prefer to see an isolator between Henley block and outgoing swa.
And a gland on the end would be a good start!

Also, that is brand new install. Dust from drilling still on ground where it fell.
Would love to see the certificate for that installation.;)
 
Last edited:
DNO won't be bothered as after their equipment. The 3m referred to above is an ESQCR Reg re main tails. This is a 'sub-main' and IMHO should have suitable protection for the cable.

Also with the cut-out on its side the electricity is prone to leaking out :D
 
An SWA with no gland, single insulated and unprotected conductors going straight to the block, doesn't look like the SWA is earthed? I assume the grey tails are feeding the original CU in the house. What is in the capping to the right?
In my opinion the SWA should be discon from the block asap.

I think the amour is all GY taped up and connected to the head.
Still a sÂŁ!$ job though.
 

Reply to Am I being over picky or is this just rough? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
816
  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
2
Replies
15
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top