I had an electrician come to do a safety check at my property that I let out last week and he has recommended that remedial work should be done at a cost of 2,100 pounds, These are:-

Upgrade of eco 7db
Upgrade of 2 x circuits to RCD protection
Install of isolation point for underfloor heating
identification of points where required
Fusing of points
Enclosure of exposed wiring - these are wires that are not in trunking
Investigation of supply wiring and condition of main isolator and repair
Retermination of required points
cable enclosures

Nothing listed but the sub total is 1,750 plus VAT comes to 2,100

Is that a lot! I last had a test done five years ago, true the wire of the economy 7 is in a situation which is not assessable, however he wants to run a wire from it across the lounge and into the kitchen!

But the amount seems excessive and it is through the Agents who manage the property for me.

Any suggestions would be very helpful.

Many thanks Surreygirl
 
As @westward10 has suggested, Mr. "Electrician" needs to bring along his copy of the regulations. This should take the form of a big yellow book (roughly A4 in size), and it is titled "British Standard. Requirements for Electrical Installations. IET Wiring Regulations 17th Edition." The standard to which it relates is BS 7671:2008 and it incorporates 4 change sets... Ammendment 1:2011, Corrigendum 2013, Ammendment 2:2013 and Ammendment 3:2015. And for each and every C1, C2 and C3 on the 'report' he should be able to point you to a regulation that is contravened and explain it to you in terms you will understand. If he can't point you to a regulation that is relevant, then as far as I'm aware it should not be listed as a C1, C2 or C3 item. It could be listed on a continuation page, but only items that can be listed as observations with the code C1, C2 or FI can result in an unsatisfactory report. It's also worth noting that an EICR should not concern itself with the building regulations compliance... for example, if at some point in the past someone has notched a joist in the wrong way, this is irrelevant.

I think the best way forward for you is to engage the services of another electrician for this meeting... someone who can quiz the guy, explain things to you if the report writer can't and who can spot if he is just full of BS.

To give better advice than has already been given without knowledge of the installation, a copy of the report and at the very least, pictures of the items to which these things relate is dam near impossible, sorry.
I agree that is what I am going to do
 
As @westward10 has suggested, Mr. "Electrician" needs to bring along his copy of the regulations. This should take the form of a big yellow book (roughly A4 in size), and it is titled "British Standard. Requirements for Electrical Installations. IET Wiring Regulations 17th Edition." The standard to which it relates is BS 7671:2008 and it incorporates 4 change sets... Ammendment 1:2011, Corrigendum 2013, Ammendment 2:2013 and Ammendment 3:2015. And for each and every C1, C2 and C3 on the 'report' he should be able to point you to a regulation that is contravened and explain it to you in terms you will understand. If he can't point you to a regulation that is relevant, then as far as I'm aware it should not be listed as a C1, C2 or C3 item. It could be listed on a continuation page, but only items that can be listed as observations with the code C1, C2 or FI can result in an unsatisfactory report. It's also worth noting that an EICR should not concern itself with the building regulations compliance... for example, if at some point in the past someone has notched a joist in the wrong way, this is irrelevant.

I think the best way forward for you is to engage the services of another electrician for this meeting... someone who can quiz the guy, explain things to you if the report writer can't and who can spot if he is just full of BS.

To give better advice than has already been given without knowledge of the installation, a copy of the report and at the very least, pictures of the items to which these things relate is dam near impossible, sorry.
I agree that is what I am going to do
do you have your own meter? if it's a supplier's meter, then anything before that is their responsibility.

if it's a landlord's meter, anything before that is up to him.

having said that, it's the responsibility of the electrician to ckeck the incoming supply and report on it's condition. remedial work would be at the cost tothe supplier or landlord as the case may be.

Yes I so have my own meter. I am not sure what cables he is talking about to be honest!
 
do you have your own meter? if it's a supplier's meter, then anything before that is their responsibility.

if it's a landlord's meter, anything before that is up to him.

having said that, it's the responsibility of the electrician to ckeck the incoming supply and report on it's condition. remedial work would be at the cost tothe supplier or landlord as the case may be.

I am the Landlord my flat has a tenant in it and I asked for a safety certificate. I have always employed an electrician myself but I left it to the Agent this time and 2100 pounds for work and also the likely hood of more. The electrician said to me that not to worry it comes out of the rent! that is why he is not worried I think. Also when I told him I found that a lot of money I happen to say I didn't like the lights so he told me he could change them for me!! It is only a studio flat. I could have the whole place rewired for that. I had rewired 10 years ago.
 
do you have your own meter? if it's a supplier's meter, then anything before that is their responsibility.

if it's a landlord's meter, anything before that is up to him.

having said that, it's the responsibility of the electrician to ckeck the incoming supply and report on it's condition. remedial work would be at the cost tothe supplier or landlord as the case may be.

OK that is good to know thank you
 
do you have your own meter? if it's a supplier's meter, then anything before that is their responsibility.

if it's a landlord's meter, anything before that is up to him.

having said that, it's the responsibility of the electrician to ckeck the incoming supply and report on it's condition. remedial work would be at the cost tothe supplier or landlord as the case may be.

OK I take that on board
 
As @westward10 has suggested, Mr. "Electrician" needs to bring along his copy of the regulations. This should take the form of a big yellow book (roughly A4 in size), and it is titled "British Standard. Requirements for Electrical Installations. IET Wiring Regulations 17th Edition." The standard to which it relates is BS 7671:2008 and it incorporates 4 change sets... Ammendment 1:2011, Corrigendum 2013, Ammendment 2:2013 and Ammendment 3:2015. And for each and every C1, C2 and C3 on the 'report' he should be able to point you to a regulation that is contravened and explain it to you in terms you will understand. If he can't point you to a regulation that is relevant, then as far as I'm aware it should not be listed as a C1, C2 or C3 item. It could be listed on a continuation page, but only items that can be listed as observations with the code C1, C2 or FI can result in an unsatisfactory report. It's also worth noting that an EICR should not concern itself with the building regulations compliance... for example, if at some point in the past someone has notched a joist in the wrong way, this is irrelevant.

I think the best way forward for you is to engage the services of another electrician for this meeting... someone who can quiz the guy, explain things to you if the report writer can't and who can spot if he is just full of BS.

To give better advice than has already been given without knowledge of the installation, a copy of the report and at the very least, pictures of the items to which these things relate is dam near impossible, sorry.

When I get home I can do that and I will upload everything and also take photographs and upload them. I do not have the facilities here
 
just a bit windy. enough to make me wind the garden parasols down.
I first read this "wind the garden parasols down" as in "wind" - weather, breeze... because of the context of the subject "windy". :oops: :D
oh... the oddities of the English language and dual purpose words!
 
By chance is he running an earth in from the E7 Board to the MET?

Tired after long day, so only briefly speed read the last 4 pages, but that's what I'm thinking is happening if I was to hazard a guess lol

He is running the cable from the main meter and the economy 7 meter to the meter in the kitchen. He is running it through the lounge because he says he cannot get to the cable running from the main metre because it is situated in an area he cannot get to and for that reason he cannot give a certificate if he cannot check what state the cable is in. So in one way he is correct although the cost is massive 2,100 pounds. He is also enclosing the grey cables in trunking and changing the fuses of the underfloor heating as he says they are the wrong ones!
 
He is running the cable from the main meter and the economy 7 meter to the meter in the kitchen. He is running it through the lounge because he says he cannot get to the cable running from the main metre because it is situated in an area he cannot get to and for that reason he cannot give a certificate if he cannot check what state the cable is in. So in one way he is correct although the cost is massive 2,100 pounds. He is also enclosing the grey cables in trunking and changing the fuses of the underfloor heating as he says they are the wrong ones!
I get the impression that this bloke is tryng it on surreygirl, watch yourself with this one, but without actual eyes on it is very difficult to be 100% sure, have you checked his credentials?
 
He is running the cable from the main meter and the economy 7 meter to the meter in the kitchen. He is running it through the lounge because he says he cannot get to the cable running from the main metre because it is situated in an area he cannot get to and for that reason he cannot give a certificate if he cannot check what state the cable is in. So in one way he is correct although the cost is massive 2,100 pounds. He is also enclosing the grey cables in trunking and changing the fuses of the underfloor heating as he says they are the wrong ones!
a lot of that looks, sounds , and smells of Bullsh!t. it looks like a duck, sounds like a duck..........
 

Reply to Am I being taken for a ride? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top