hi just looking for some advice.

I have c&g in:-
2360 part 1
2360 part 2
2377 pat testing.
3666 optical fibre.

The 2360 part 1 & 2 are 5 years apart.
The part 2 I have
assignments part 2 pass
Installation, commissioning,and fault diagnosis credit
Electrical, science and principles credit.
I believe I need a completion cert for full part 2.

What would be my next step?
 
1.3 Electrician

Qualification and Training
Must satisfy the following conditions:-
(1) Must have been a registered Apprentice or undergone some equivalent method of training and have had adequate practical training in electrical installation work.
(2) Must have obtained an NVQ Level 3 in electrical installation work (or approved equivalent) - see Note 1.
(3) Must have obtained a pass in the City & Guilds 2360 Electrical Installation Theory Part 2 Course Certificate or the EAL Diploma in Electrotechnical Services (500/3526/5) (or approved equivalent).
Note 1: If the applicant meets the other two criteria but has not achieved an NVQ Level 3 in electrical installation, then a "Provisional" grading may be awarded if the following criteria are both satisfied:
(a) have obtained at least the City & Guilds 2360 Electrical Installation Theory Part 2 Course Certificate or EAL Doploma in Electrotechnical Services (500/3526/5) (or approved equivalent)
(b) have obtained Achievement Measurement 2 or must be able, with the application for Grading and any other relevant supporting evidence (i.e. the City & Guilds Electricians Certificate) which may be required, to satisfy the Grading Committee of his experience and suitability.



do you mean qualified in the eyes of the jib?

if so, this is off the jib website. it says you'll get a provisional grading, until you get the nvq. but remember, in the eyes of the law you also need to be competent. if you want the 2356 nvq level 3, you'd better get your finger out, cos it's getting yanked in less than a fortnight. good luck.
 
Upvote 0
Hi stokesie,

In order to become a qualified electrician you need:

City and Guilds 2365 Level 3 Diploma in Electrical Installations (Buildings and Structures) or if you can sign up for an apprenticeship then the City and Guilds 2357 NVQ Level 3 Diploma in Installing Electrotechnical Systems and Equipment (Buildings and Structures)
City and Guilds 2382 the 17th Edition of the Wiring Regulations BS 7671 (Requirements of Electrical Installations)
City and Guilds 2394 Level 3 Award in the Initial Verification and Certification of Electrical Installations
City and Guilds 2395 Level 3 Award in the Periodic Inspection, Testing and Certification if Electrical Installations


So in short, you are not a fully qualified electrician yet.

I reccomend visiting the JIb website or looking here for more info.
 
Upvote 0
2330 level 2 or equiv
2330 level 3 or equiv
2356 NVQ 3 or equiv
AM2 or equiv


you do not need 2394 -2395 to be graded as an electrician. You will need this to become an approved electrician !
 
Upvote 0
the lads doing apprenticeships have to do am2. if you're an adult on the 2356 you don't need it - you can get a jib card without it.
 
Last edited by a moderator:
Upvote 0
i tend to find that if you have to ask "am I qualified ?" , then you're probably not.

and i wouldnt rely solely on a list of C&G numbers as a means of defining status , there is a element known as "work experience"
;-)
 
Upvote 0
In reply to the last post, I was an apprentice from leaving school for 5 years but did not take my part 2 exam due to being made redundant. I then worked on cable tv for 3 years before going back to college and completing my part 2 and doing the pat testing course. At this point I was house bashing for 2 years before working as a maint electrician in a factory. I was made redundant after 2 years then changed my career to working on the motorway network comms and fibre splicing, power etc...
I am still on the motorways looking after comms infrastructure, the job is now changing a bit as we are looking after some power infrastructure, which is the reason for wanting to get my sparky status.
 
Upvote 0
In my day the 2360 came in A), B), C). B and C i seem to remember came in as a single examination taken in two parts... Maybe someone here can verify that or not??
I would also state that the 2360 was superior to the 2330 that replaced it, but that's my opinion. lol!!


At least in those day's examinations were just that. No multiple choice questions then, all were set questions that you had to know and provide the calculations and/or descriptive answers to substantiate. I don't think i've ever sat an open book examination ever!! lol!! And another thing, in those early day's calculators were not allowed in the examination room either!!

You lot don't realise just how easy you have it these day's...lol!!
 
Upvote 0
i'd be hard pressed to argue with you e54. i did the 2330 and it was very easy. even so, when i was at college, i saw lads who were clearly out of their depth but, still managed to blag their way through the exams. personally, i'd do away with the multiple choice exams; when you dumb down to the levels that city and guilds have, it can only serve to harm the electrical industry.


i read somewhere that the 2360 was scrapped because it was too hard. then, i think they replaced it with the 2351(?) which wasn't well received by the industry. so, they tried again with the 2330 (apparently better than 2351 but not as good as 2360). now they're doing it again, with the 2391 - scrapping it because it's 'too hard'.
scrapping something because it's too hard doesn't make much sense to me, especially when you're dealing with electricity. the more cynical side of me tends to think it's more to do with money but any short term monetary gains they make, will be far outweighed by the long term negative effects that it has on the electrical industry. saturating the country with sub-standard, under trained electricians is a recipe for disaster.
 
Upvote 0
In my day the 2360 came in A), B), C). B and C i seem to remember came in as a single examination taken in two parts... Maybe someone here can verify that or not??
I would also state that the 2360 was superior to the 2330 that replaced it, but that's my opinion. lol!!


At least in those day's examinations were just that. No multiple choice questions then, all were set questions that you had to know and provide the calculations and/or descriptive answers to substantiate. I don't think i've ever sat an open book examination ever!! lol!! And another thing, in those early day's calculators were not allowed in the examination room either!!

You lot don't realise just how easy you have it these day's...lol!!

236 came in parts A ( 1st year ) , B ( 2nd year ) and C ( optional 1 year Technicians course)
2360 ( introduced around 1990 ) came in parts 1 , 2 & 3 (C) , which is the course i completed at tech.
written exams for each year were indeed in 2 parts , 4-5 hours in total from what i can barely remember lol
 
Upvote 0
Please anyone show me legislation that proves beyond doubt that anyone that starts a business TOMORROW as a ' Qualified Electrician' can be prosecuted for trading as as an 'Electrician' ? If this was the case the courts would be full...My Nan could start up tommorrow as an 'Electrician'...if she injured someone that's a different kettle of fish...Qualification in its self means nowt...Just look at the Electrical Trainee's ?
J
 
Upvote 0
Please anyone show me legislation that proves beyond doubt that anyone that starts a business TOMORROW as a ' Qualified Electrician' can be prosecuted for trading as as an 'Electrician' ? If this was the case the courts would be full...My Nan could start up tommorrow as an 'Electrician'...if she injured someone that's a different kettle of fish...Qualification in its self means nowt...Just look at the Electrical Trainee's ?
J

Wrong ...Qualifications are a MUST HAVE they are certified proof that you have successfully completed a specified course!! However, it really does need to be the right qualifications to make any sense holding them. A perfect example are those pointless qualifications that 17 day whizzer's and electrical trainee's hold. These would hold little to no meaning without a recognised base qualification!!

As for the rest of your post, ...You can thank all the parasitic organisations that have been left to get a strangle hold within the electrical industry. You are now nothing more than cheap labour and cash cows, to be passed around as they please by these leeches...
 
Upvote 0
Wrong ?..Then point me to legislation as I already have asked that says I have to have qualifications to carry out electrical work ? The only legislation I can find that would cover our work is EAWR, and I can find nothing in there that says you MUST have formal qualifications, would you get a job on the cards or on site without them ?..Probably not...but to trade as an electrician I don't believe you do..well register with a scam provider maybe..lol !
 
Upvote 0
legislation requires you to be 'competent' and, as we can see on another thread right now (scam questions), not everyone's in agreement as to how we should be able to prove 'competency'.


bs7671 has a paragraph on it though, and they think you should have qualifications.



edit: alright, i'm on my 8th can... i know they don't mention qual's specifically, but qualifications are a good indication for proving technical knowledge......did i say i was on my 8th can??
 
Last edited by a moderator:
Upvote 0
legislation requires you to be 'competent' and, as we can see on another thread right now (scam questions), not everyone's in agreement as to how we should be able to prove 'competency'.


bs7671 has a paragraph on it though, and they think you should have qualifications.

I agree completely...Competent yes...but Qualified doesn't necessarily mean competent BS7671 isnt law EAWR is..as EAWR states....




Persons to be competent to prevent danger and injury
16. No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work.

J
 
Upvote 0
my 2p jimmy ,

there is no law or requirement to be "qualified" in any way to carry out electrical work of any kind , so theres no point in looking for a definitive definition in what constitutes "qualified" , unlike in the medical and legal professions which have clear criteria.
instead the electrical indusrty relies on the wishy-washy term "competent" which can be considered a combination of experience , training and qualifications.
of course the full extent of your competency can only be measured / proved if you have the misfortune to be up in court cos things have got "bent".

so there it is.
;-)
 
Upvote 0
Ok. Just to clarify.... I'm more than half way through 2365 L2 at the moment.

Now all I will need after that is:
* 2365 L3;
* 2357 NVQ (I believe this is the new 2356, and is available at my college);
* NET AM2 Assessment.

So after successfully completing all of the above, I can then register as a qualified electrician and carry out work?

Only problem I may have here is that the 2357 NVQ requires me to enrol as an apprentice, which is a problem because I work for my old man as a labourer and also carry out small electrical work such as disconnecting down-lights and reconnecting after plastering, changing transformers, installing new light switches ect. I can only assume this is not enough to qualify as an apprentice, and it's so hard to find anyone willing to take on apprentices!
 
Upvote 0
Ok. Just to clarify.... I'm more than half way through 2365 L2 at the moment.

Now all I will need after that is:
* 2365 L3;
* 2357 NVQ (I believe this is the new 2356, and is available at my college);
* NET AM2 Assessment.

So after successfully completing all of the above, I can then register as a qualified electrician and carry out work?

Only problem I may have here is that the 2357 NVQ requires me to enrol as an apprentice, which is a problem because I work for my old man as a labourer and also carry out small electrical work such as disconnecting down-lights and reconnecting after plastering, changing transformers, installing new light switches ect. I can only assume this is not enough to qualify as an apprentice, and it's so hard to find anyone willing to take on apprentices!


it will make you a j.i.b gold card electrician yes and opens more doors than just a 1/Electrical Trainee person
 
Upvote 0
Cheers for your reply John. Nice to know I'm spending my time wisely by doing the right courses. It's hard to get a simple, straight answer out of my college! Is it true there is a 2365 L4 course or is that another college rumour out of all I've heard?

What's a 1/Electrical Trainee person?

Also Is is correct to do the AM2 as the last thing or can I do it after completing 2365 L3?
 
Upvote 0
Electrical Trainee is a 5week wonder....these people are becoming competent electricians and are taking the mick out of people like you and me who are doing it / have done it the proper route - yes i realise you're not doing a proper apprentership, which i can understand are hard to come by these days - but you are doing the next best thing, and the qualifications you recieve from doing the full time course are pretty much the same as the apprentership without the infield experience - and for this, skamuk i salute you.

Was just wondering how you're going to be able to do your NVQ though without having an apprentership?

AM2 i think is the last course you take at college yes, your tutor will be able to tell you what dates you will be sitting it. You'll sit the AM2 whenever your college teacher thinks you're ready (i think, don't quote me on this)

After you've done the couses that you have listed, you should think about doing the 2394 and 2395 testing qualifications.
 
Upvote 0

Reply to Am I "Qualified" a electrician ? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
Unfortunately, I didn't get it resolved so I have had to complete the C&G 2346 Experienced worker course, which is basically a work place logbook...
Replies
6
Views
3K
  • Question
It is a complex situation - contact Napit/Niceic/Stroma etc and ask what they need for you to join and they will be keen to have an advisor...
Replies
1
Views
2K
  • Question
Really all depends on what role they are taking on. Lamp changer? Domestic, Commercial, or industrial? Street lighting and so on. The current...
Replies
14
Views
3K
Hi Bill. Yeah, there is and I have contacted a couple of firms working there. I'll see how that goes. But would like to end up being my own boss...
Replies
2
Views
1K
  • Question
That makes sense, it's the reality I suppose. Like you said, a means to an end and if they don't want to budge then I understand that!
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks