I am taking my AM2 in 8 weeks and have some questions that I was hoping you guys could answer for me?
1. Does the pre-installed metal containment require earthing?
2. When wiring the RFC do you follow the specification (with a long leg from the final socket-outlet back to the board or can you wire it so that that you keep the cable runs relatively equal?
3. Do you need to sleeve/identify the numbered cores on the SY cable for the motor circuit?
4. If the external socket-outlet is to be fed from the FCU, do you connect it to the load side (protected by the 13A fuse)?
5. What exactly is a bridging section when installing Cat5 cable in multi-compartment PVC trunking as I have not seen one before?
6. Is it okay to ask the assessor for the DNO Ze value or are you expected to measure it?
7. Is the luminaire usually a 2D 28w?
Thanks
 
You need to follow the specification, just like the real world, failing to follow the specification will result in lost marks.
You also need to demonstrate your knowledge and understanding of the wiring regulations, some of the questions you ask suggest that maybe your knowledge isn't quite enough to be taking this exam just yet.

5. A bridging section is a piece of plastic fitted in to the LV compartment to allow ELV cables to pass through it without coming in to contact with the LV cables.
6. You measure it.
7. Don't know, but the type of light fitting shouldn't have any bearing on your install.
 
You need to follow the specification, just like the real world, failing to follow the specification will result in lost marks.
You also need to demonstrate your knowledge and understanding of the wiring regulations, some of the questions you ask suggest that maybe your knowledge isn't quite enough to be taking this exam just yet.

5. A bridging section is a piece of plastic fitted in to the LV compartment to allow ELV cables to pass through it without coming in to contact with the LV cables.
6. You measure it.
7. Don't know, but the type of light fitting shouldn't have any bearing on your install.
The spec apparently shows 2x main equipotential bonding conductors to the gas and water services, however, you ARE allowed to run one continuous 10mm2 length instead. This is not following the spec but IS allowed.
With regards to the luminaire, the reason I ask is because of the maximum demand/diversity calculation. ie If it was a discharge fitting then I would have to apply 1.8
 
Follow the spec. It’s quite easy just stressful

I agree with it being easy, but I didn't find any part of it stressful.
[automerge]1583080397[/automerge]
The spec apparently shows 2x main equipotential bonding conductors to the gas and water services, however, you ARE allowed to run one continuous 10mm2 length instead. This is not following the spec but IS allowed.
With regards to the luminaire, the reason I ask is because of the maximum demand/diversity calculation. ie If it was a discharge fitting then I would have to apply 1.8

I dont like that, if a contractor ignored the spec like that on a job without written permission I'd make them redo it at their own cost.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
AM2 ADVICE
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
andrew8902,
Last reply from
casperLennon,
Replies
5
Views
2,079

Advert

Back
Top