D
Deleted member 105166
...nor the test leads and (most importantly) nor the person whose neck said meter is hanging around!there's no way a meter is going to survive even a modest PFC flowing through it.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss AM2 testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
...nor the test leads and (most importantly) nor the person whose neck said meter is hanging around!there's no way a meter is going to survive even a modest PFC flowing through it.
...nor the test leads and (most importantly) nor the person whose neck said meter is hanging around!
Yes it has the setting and displays the values, mine does too, but it doesn't measure the PFC, it calculates it from the measured loop impedance and voltage. This is made clear in the manual.
To actually measure the PFC you would have to allow that current to flow, and there's no way a meter is going to survive even a modest PFC flowing through it.
Hopefully whatever is around your neck is not a conductor that would hurt lol im pretty sure no manufacturer of testers would design anything to conduct electric around your neckAs much as I know my tester is designed with safety in mind I always avoid carrying out a live test with it hanging round my neck.
Obviously, although what @davesparks said makes good sense and I'll certainly adopt it, as if a tester is going to fail and go 'bang', I'd rather that happen with it anywhere other than against my own body!Hopefully whatever is around your neck is not a conductor that would hurt lol im pretty sure no manufacturer of testers would design anything to conduct electric around your neck
i trust my tester to not kill me even if it went bang and blew itself to bits.Obviously, although what @davesparks said makes good sense and I'll certainly adopt it, as if a tester is going to fail and go 'bang', I'd rather that happen with it anywhere other than against my own body!
Hi I did my am2 last week
Ze just measure each phase to earth and record the highest reading
We were told didn’t need to do pefc just pscc done same as ze except test between each phase and neutral then double highest one and record reading, were ever it says ze db just write your ze in.
You do polarity between all phases to earth, all phases to neutral, between all phases and neutral to earth, ze, pfc, phase sequence at board, then power on, phase rotation at each 3 phase circuits, rcd test then calculate your zs for each circuit.
Do functional tests and u have to write all calculations down
ive got my am2 next week im pretty much comfortable with everything apart from live testing as ive done it once about 2 years ago. I'm unsure on tester settings 2 lead low/ 2 lead high / 3 lead high /3 lead lowAsk them before you do the test. Where I did it they had a switch where they could bypass the rcd when testing in the bays
ive got my am2 next week im pretty much comfortable with everything apart from live testing as ive done it once about 2 years ago. I'm unsure on tester settings 2 lead low/ 2 lead high / 3 lead high /3 lead low
fantastic thats really helpful! presence of a rcd in a circuit? the its going to be a 3p&n mainswitch. I've been told we are testing from the supply side of the mainswitch so it wouldnt matter about the presence of rcds?High current tests should be used whenever possible as they give the most reliable result.
A 3 lead low current test should only be used when the presence of an RCD in a circuit prevents high current tests.
A 2 lead low current test will be the least reliable and should only be used when no other method is possible.
thanks buddy!!High current tests should be used whenever possible as they give the most reliable result.
A 3 lead low current test should only be used when the presence of an RCD in a circuit prevents high current tests.
A 2 lead low current test will be the least reliable and should only be used when no other method is possible.
Yes as far as I’m aware you’re correct I’ve always measured my Ze and PFC at supply side of main switch with a 3 lead High setting so Rcds should not come into effect. I take the main earth out of the earth bar and do it that way to avoid parellel paths and give true reading.fantastic thats really helpful! presence of a rcd in a circuit? the its going to be a 3p&n mainswitch. I've been told we are testing from the supply side of the mainswitch so it wouldnt matter about the presence of rcds?
[automerge]1569866453[/automerge]
thanks buddy!!
Yes as far as I’m aware you’re correct I’ve always measured my Ze and PFC at supply side of main switch with a 3 lead High setting so Rcds should not come into effect. I take the main earth out of the earth bar and do it that way to avoid parellel paths and give true reading.
fantastic thats really helpful! presence of a rcd in a circuit? the its going to be a 3p&n mainswitch. I've been told we are testing from the supply side of the mainswitch so it wouldnt matter about the presence of rcds?
[automerge]1569866453[/automerge]
thanks buddy!!
Right ok IA high current test is a 2 wire test, it doesnt need the additional neutral connection that the low current tests require.
[automerge]1569876563[/automerge]
K
If the supply to the board has an RCD further upstream, which it may do in a college enviroment, then you would still have to use a low current test. You will have to ask the person supervising your AM2 about this as it will vary between test centres, as someone mentioned earlier some of them will be able to bypass the RCD temporarily for the test.
Right ok so just to clarify are the results I’m obtaining wrong by carrying out the 3 lead test (high) with the neutral?A high current test is a 2 wire test, it doesnt need the additional neutral connection that the low current tests require.
[automerge]1569876563[/automerge]
K
If the supply to the board has an RCD further upstream, which it may do in a college enviroment, then you would still have to use a low current test. You will have to ask the person supervising your AM2 about this as it will vary between test centres, as someone mentioned earlier some of them will be able to bypass the RCD temporarily for the test.
Reply to AM2 testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net