The board will be locked off at all times when the board cover is off so u can only do it on the supply side
You won’t be doing zs they will all be calculated, you can do on the sockets if u want but it’s pointless and a waste of time cause you only have to write down the calculated zs for all circuits anyway and also show your calculations
Okay yeah supply side is what I thought. So if it’s 3p&n
Earth fault loop impedance:
Setting on tester: L-PE and Max Z
Disconnect main earth and test between
L1-N-E
L2-N-E
L3-N-E
Re-connect main earth
Taking the highest reading and writing it in Ze
PFC
Setting on tester L-PE Max Z
L1-N-E
L2-N-E
L3-N-E
Taking the highest reading in KA and X2 to get the fault current of potential 2 phases recording it in KA ensuring it doesn’t exceed circuit breaker capacity’s
ZS
Mainswitch and 32a ring main to be turned on if safe to do so
The only live test that can be done is Zs at the sockets if a RCD is present ensure multi function tester has been set to no rcd trip to avoid nuisance tripping taking the highest Zs value which is normally the furthest socket recording it in the appropriate box
RCD
Ensuring to test both sides of the sine wave 0-180 degrees
1/2 second
1 second
5 seconds
And function test of the RCD
Functional test of all equipment once all covers have been installed back on.
Does this look right to you or can you correct me on anything?