I've got my AM2 in Liverpool on Tuesday, good luck mate. GN3 and OSG aren't very good for 3-phase testing procedures, for example insulation resistance and pfc/psc test methods aren't described at all. For the IR tests you need to test between 10 combinations same as safe isolation. PFC can anyone explain how to do this on a 3-phase board? Also on the schedule of test results what ref. method do we put down?
For PFC just consider the board as three single phase installations (that just happen to use the same earth and neutral).

For each line conductor you test the earth fault current and the short circuit current.

The results should be similar.

You would record the highest value you measure of the earth fault currents as the prospective Earth Fault Current.

For the short circuit current because the Line to Line short circuit current will be higher than the Line to Neutral short circuit current, but you have measured only the Line to Neutral short circuit current (because it will be dangerous to test Line to Line unless the tester is suitably rated for this), as a rule of thumb you double the measured value of the Line to Neutral Current and record the highest of these values as the prospective short circuit current.


The reference method is the one used for the installation of the cabling for the relevant circuit:
Enclosed in conduit in thermally insulating wall A
Enclosed in conduit or trunking on a wall B
Clipped direct C
Direct in ground or in ducting in ground, in or around buildings D
In free air or on perforated cable tray E
In free air or on perforated cable tray F
In free air, flat spaced by 1 cable diameter G
4D5 (Twin & Earth) cable above a plasterboard ceiling covered by thermal insulation not exceeding 100mm in thickness 100
4D5 (Twin & Earth) cable above a plasterboard ceiling covered by thermal insulation exceeding 100mm in thickness 101
4D5 (Twin & Earth) cable in a stud wall with thermal insulation with cable touching the inner wall surface 102
4D5 (Twin & Earth) cable in a stud wall with thermal insulation with cable not touching the inner wall surface 103


Good luck with your AM2.
 

Reply to AM2 Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
534
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K
  • Question
I’d say yes go for it.
2
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top