J
jerrybouncer
Good luckwith your exam. Relax and you'll be fine!!
dont get too excited the next part of the question got me puzzled
State
i. a suitable observation to be recorded on the periodic report if the voltage drop fails to comply
ii. one action which could be taken to rectify the situation in i. above
i. circuit blah blah failed volt drop test code 2
ii. reduce length of circuit?
Hi matehave i got this right, i know this has already been discussed somewhere but wanted to try it off the top of my head
sorry to be a pain in the butt
during the course of the inspection one of the single phase radial circuits supplying an item of fixed electrical equipment is to be checked for voltage drop compliance. The circuit has the following characteristics
load current = 45 amp
circuit length = 80 metres
live conductors = 10mm
a. using the information given in figure 1 determine whether the circuit meets the requirements for voltage drop. Show all calculations
80 x 1.83 x 2 x 1.2/1000 = 0.35136
v = ixr
vd = 45 x 0.35136 = 15.8 volts
230v circuit 5% = 11.5 volts
so circuit does not comply
is this correct?
state the test to be carried out to ensure safety before testing the rcbo 2 marks
hummed and harred for 20 minutes this was the last question, i put Ze then scribbled it out and put PFC
I put functional test of intergral test button!!
correct here aswell. Finished the exam with an hour to go, just went over everything again. Feel if i dont do this one i need shooting!
I think the answer shoud Zs as this verifies the presence of a circuit protective conductor in the first place. No cpc no effective operation