A BS EN 60898 circuit breaker has an lcn of 10 kA and an Ics rating of 6 kA.
State
a) how the circuit breaker is likely to perform if the circuit developed a fault current of 8kA (1 mark)
b) the likely operational condition of the circuit breaker following the fault (1 mark)
c) the action that would need to be taken to ensure the circuit was protected should a similar fault occur in the future. (1 mark)

This is one topic i have not covered in depth, correct me if i am wrong here

Uo/Zs = Ia
 
A BS EN 60898 circuit breaker has an lcn of 10 kA and an Ics rating of 6 kA.
State
a) how the circuit breaker is likely to perform if the circuit developed a fault current of 8kA (1 mark)
b) the likely operational condition of the circuit breaker following the fault (1 mark)
c) the action that would need to be taken to ensure the circuit was protected should a similar fault occur in the future. (1 mark)

This is one topic i have not covered in depth, correct me if i am wrong here

Uo/Zs = Ia

Ics is the max fault value that a device can clear and be put back into service again.

Icn is the max fault value that a device can clear but the device will not function again.

A) The device will interrupt the fault.

B) The device will not be operational.

C) The protective device should be replaced.
 
Ics is the max fault value that a device can clear and be put back into service again.

Icn is the max fault value that a device can clear but the device will not function again.

A) The device will interrupt the fault.

B) The device will not be operational.

C) The protective device should be replaced.

i have just paid for a copy of the regs online so i will have a bit of reference material, so the circuit breaker would be faulty, thanks

i have been looking in gn3 for information on 100mA rcds, i know they are tested at times half and at times 1 but i cant find any info on tripping times, if i remember correctly its 200 ms for the bs one and is it 300 ms for 61009
 
Just remember BS EN RCD have 300ms trip time

BS numbered RCD is 200 ms..

Remember the EN as extra time to trip.

You only do the 5x test on 30mA RCD

thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky
 
Last edited by a moderator:
Value of resistivity for 1.5mm = 12.10 milliohms per metre
Value of resistivity for 10mm = 1.83 milliohms per metre

Therefore (R1&R2) resistivity in milliohms per metre = 12.10+1.83 = 13.93 milliohms per metre
Length = 28m
Factors = 1.02 & 1.20 (from tables 9B and 9C OSG)

Therefore, R1&R2 = (milliohms per metre x Length x Factor) / 1000

= (13.93 x 28 x 1.02 x 1.20) / 1000 = 0.48 ohms.

Zs = Ze + (R1&R2)

= 0.14 + 0.48 = 0.62 ohms

I have been thinking about this.
Value of resistivity for 1.5mm = 12.10 milliohms per metre
Value of resistivity for 10mm = 1.83 milliohms per metre

Therefore (R1&R2) resistivity in milliohms per metre = 12.10+1.83 = 13.93 milliohms per metre
Length = 28m

I agree, these figures are taken from table A.1 and are the value at 20C
Therefore at 20C our circuit resistance would be
13.93*28/1000 = 0.39 Ohms.

We have designed the circuit at 25C so if we were to measure the R1+R2 value at 25C we would need to add a correction factor because at 25C the resistance would be slightly higher, this correction factor is 1.02.
So the realistic resistance figure at 25C for our circuit would be:
.39 Ohms * 1.02 = 0.398 Ohms

This is what the correction factors for ambient temperature are for, they are to be applied to the tables EG table A.1 to change the values in those tables measured at 20C to whatever temperature the circuit is being measured at in reality.

Now The rule of thumb (the .8 rule) is used to multiply the tabulated figures in BS7671 which are measured at 70C
The 0.8 is used to bring the figures measured at 70C down to a figure that they would be if the circuit were measured at 20C.
Conversely if we want to convert our figure of R1+R2 measured at 20C to a figure measured at 70C we would multiply it by 1.2 this figure would then become our R1 + R2 measured at 70C and we would add Ze to this. We would then be able to compare this figure directly to the tables in BS 7671.

So in this instance we need the figure for the circuit we are designing, the R1 + R2
measured at 20C.
We calculate what this figure is by using the above formula EG:
13.93*28/1000 = 0.39 Ohms.
This is the figure at 20C.
We then multiply the figure at 20C by a factor of 1.2.
0.39 * 1.2 = 0.468 Ohms.
Add this to Ze
Zs = .14 + .468 = 0.608 Ohms.
This is the figure we would use to compare to figures in BS 7671.
We would not use the ambient temperature figure in this calculation.
The only time we would use the ambient temperature correction factor of 1.02 was if we were measuring our R1+R2 at 25C and we needed to compare these measured figures with those in the book which were recorded at 20C
We would take the figures in the book measured at 20C multiply them by a factor of 1.02 and this would give the value of the table figures at 25C.
We would then be able to compare our measured reading at 25C directly to these tabulated figures.
We would not use both the factors of 1.02 and 1.2 together in the same calculation.

This is how it appears to me, shoot me down if I am wrong.

One more thing, I noticed a nice little fact today.
The resistance of copper will increase by 2% for every 5C increase in temperature.
So if in doubt use this way to measure what the resistances would be at different temperatures.
If a cable increases in temperature from 20C to 70C its resistance will increase by 20%
 
Last edited:
thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

B is also 5% I think, it's not a lighting circuit so it is 5%

I do not know the reason for the difference in the 3% and the 5% I just know it's a fact set in stone so I don't argue with it.
 
thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

It's 8% from a private supply source.

The reason for the lower level for lighting is that some types of lighting cannot strike up on lower voltages so tolerances are tighter.
 
Last edited:
Hi

for single phase 3% for lighting 6.9v
5% for power circuits and distribution 11.5v
and for the answer to b) its 20V which is 5% of 400v

no sorry i am wrong its not 20V as its there own supply not sure
 
thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

Have a look at Appendix 12 in BS 7671 it covers VD only.
 
Hi

for single phase 3% for lighting 6.9v
5% for power circuits and distribution 11.5v
and for the answer to b) its 20V which is 5% of 400v

no sorry i am wrong its not 20V as its there own supply not sure

I'm guessing it's 5% per phase so it's 11.5V at each phase where the equipment is installed, not measured between phases.
But I'm guessing.
Sorry it's 8% from a private supply source (This is a new one for me) so I am guessing it is 8% per phase = 18.4 V
But it's just a guess so hopefully I'll be put right by someone.
 
Last edited:
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.
 
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.

Spot on, the percentage is actually of 400 Volts ie. 32 Volts
 
the loop length for circuit 1 is 50 m long the ze is is 0.11 ohms

determine showing all calculations the r1 + r2 and the expected zs

7.41 x 50/1000 = 0.37 12.10 x 50/1000 = 0.60

zs = ze + (r1 = r2)

0.11 + (0.37 + 0.60) = 1.08

have i done this correctly?
 
Last edited by a moderator:
the loop length for circuit 1 is 50 m long the ze is is 0.11 ohms

determine showing all calculations the r1 + r2 and the expected zs

7.41 x 50/1000 = 0.37 12.10 x 50/1000 = 0.60

zs = ze = (r1 = r2)

0.11 + (0.37 + 0.60) = 1.08

have i done this correctly?

I can't confirm the mOhm values but the maths is correct.

You MUST use (R1+R2) when doing these calculations and remember that r1, rn and r2 are reserved for ring continuity figures, this exam is very big on correct terminology.
 
Hang on, is this a ring final circuit?

yes i just shortened the question the m/ohm/ for 2.5 is 7.41 and 1.5 is 12.10

i am not great at the terminology but i am getting there with the calculations

in some crazy way i am actually finding the long questions easier than the short ones atm
 
If it's a ring then the R1+R2 value is r1+r2/4

R1+R2=0.37+0.60/4

R1+R2=0.24 Ohms

Zs=(R1+R2)+Ze

Zs=0.35 Ohms
 
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.

just ordered a set of regs from fleabay so they should be with me in the next couple of days - the only problem i found with the regs in the past was navigating them, i always favoured the on site guide for obvious reasons
 
If it's a ring then the R1+R2 value is r1+r2/4

R1+R2=0.37+0.60/4

R1+R2=0.24 Ohms

Zs=(R1+R2)+Ze

Zs=0.35 Ohms

no thats for your cross connections isnt it are you not thinking of step 2 of ring final circuit continuity? now i am really confused

your end to end resistances are your r1 and r2 values
 
Last edited by a moderator:
If you are asked to calculate R1+R2 on a ring final circuit and you are given the 'loop length' then you need to divide the end to end continuity readings for r1 and r2 by 4 to arrive at a figure for R1+R2.

It's actually mentioned in step 3 of the continuity of ring final conductors test (if you were measuring R1+R2 then you would not need to divide by 4).
 
Last edited:
If you are asked to calculate R1+R2 on a ring final circuit and you are given the 'loop length' then you need to divide the end to end continuity readings for r1 and r2 by 4 to arrive at a figure for R1+R2.

what a d**k! of course, i keep getting caught on the little things so basically there was about 10 marks down the drain

LOOP LENGTH

(0.37+0.60)/4 = 0.24 + 0.11 = 0.35
 
Last edited by a moderator:
what a d**k! of course, i keep getting caught on the little things so basically there was about 10 marks down the drain

LOOP LENGTH

Scan the question twice, find out EXACTLY what you've been given and EXACTLY what they're asking.
 
these questions are all simple in theory, but a nightmare in principal lol

It'll just click once you know the formats and double check the questions.

Also remember that on longer testing questions, if you fail to mention say deducting test lead resistances before a continuity test, even though you may go on to describe the rest of the process perfectly, your end result would be incorrect so answers are heavily penalised in that scenario.
 
yes mate practice writing test procedures over and over then you will have it nailed

Iq is spot on as usual

you miss a important part of test procedure and will get no further marks for that question

and when doing r1,r2,rn the r2 will always be slghtly higher for T/E as the cpc is smaller so resistance will be higher approx 2.5/1.5mm = 1.67 times higher
so you R1 +R2 will be slightly higher than the R1 + RN value

and like he says read the question a couple of times until your sure you know what they are asking before answering
 
Last edited:
i have looked at that many questions in the last four days my head is fryed but thats the advice i was given - read gn3, then read it again, then read it again, and keep going over previous exam papers, i have just ordered on site guide as well
 
also have a look at GS38 which is for test instruments eg finger guards 4mm probe tips preferably 2mm
also memorandum of guidance on elecy at work regs i have it in pdf if you want it as some of these come up
when you get the regs read part 6 and especially 7 zones for fountains bathrooms etc
100mA rcds sockets outlets in agricultural
300mA rcds protection aginst fire in agricultural
500mA rcds sockets on construction sites
a few questions come up out of part 7 special locations
locations containing baths or showers
rooms containing sauna heaters
swimming pools and other basins

learn IP ratings
protection against water
Ipx8 protection against continous submersion
ipx7 protection against temporary submersion eg min for zone 0 bath
ipx6 protection against powerful water jets
ipx5 protection against water jets
ipx4 protection against splashing water
ip3x protection against spraying water
ip2x protection against dripping water when tilted up to 15degrees
ipx1 protection against dfriping water

protection against objects

ip6x dust tight
ip5x dust protected
ip4x protection againstsolid objects greater than 1mm and protection against 1mm wires for horizontal top surface eg CCU tops of sockets, enclosures etc solidobjects
IPXXD is same but only protection against 1mm wires
ip3x against solidobjects greater than 2.5mm
ip2x protection against solid objects greater than 12mm eg your finger or a standard test fingr and small rocks stones etc
ip1x protection against 50mm solid objects eg hand

IpxxA protection against large part of body
ipxxb protection against contact by standard test finger only
ipxxc protection against tool eg screwdriver
ipxxd protection against contactby 1mm wire
 
Last edited:
tell you where i am struggling conductor and insulation resistance

what happens to conductor resistance if a cable length is increased etc etc

i keep getting them wrong time after time

oh and the schedules of circuit details the one you stick in the door on the db

list 5 items - ermmmmm?
 
increase length increase resistance half length half resistance or double Csa half the resistance

insulation resistance NO change

the schedule of test results is that what your referring to
 
Last edited:
existing installation, new garage built - what information would you require to carry out the verification

The results of the general assessment of characteristics sections 311,312 and 313
Any plans, charts or drawings relating to the installation

Is this an acceptable answer or do i need to list them separately ie earthing arrangements, max demand, supply protective device characteristics, rating of consumer unit etc
 
increase length increase resistance half length half resistance or double Csa half the resistance

insulation resistance NO change

the schedule of test results is that what your referring to

has anybody got a copy of one of these?
 
it sounds like nerves are getting the better of you so you are second guessing all of the stuff you already know which is making you more nervous. Set aside a couple of hours each night and get to grips with the terminology (thats the biggest confusion in my eyes) and by the time your retake your exam, it will come to you. Don't let dread of the exam block the knowledge that you quite clearly have already
 
Stick with the link Jud has posted, the 2391-10 is based only on these model forms, NICEIC etc are very different.

By the time you get familiar with the forms, take your exam and get your results, you should have a few weeks before the Electrical Installation Condition Report consigns the Periodic Inspection Report to the bin ;)
 
http://electrical.------.org/wiring-regulations/forms/2008.cfm?type=pdf

thanks i am not sure if the form i am looking for is in there, its the one with all the circuit details you see inside the door of distribution boards after the test has been completed and it lists the circuit details not so much the test results
 
it sounds like nerves are getting the better of you so you are second guessing all of the stuff you already know which is making you more nervous. Set aside a couple of hours each night and get to grips with the terminology (thats the biggest confusion in my eyes) and by the time your retake your exam, it will come to you. Don't let dread of the exam block the knowledge that you quite clearly have already

so my original answer is ok? not to list the items individually
 
thanks i am not sure if the form i am looking for is in there, its the one with all the circuit details you see inside the door of distribution boards after the test has been completed and it lists the circuit details not so much the test results

You're thinking of a 'schedule of circuit details' this form does not exist in 2391 land, it's an NICEIC etc. type form that also gets used as a DB schedule.
 
You're thinking of a 'schedule of circuit details' this form does not exist in 2391 land, it's an NICEIC etc. type form that also gets used as a DB schedule.

yes there is actually a question on this in the 2391, i saw it somewhere a few days ago and it had me on the ropes, i want to go over the question again, it asked you to mention 5 items from the sheet, dont quote me on this it was something along the lines of number of points, isolation and switching...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
An Awful Feeling This
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
350

Thread Tags

Advert

Thread statistics

Created
gap30,
Last reply from
trev,
Replies
350
Views
35,862

Advert

Back
Top