Hi chaps, This is part looking for advice, part moan. Bear with me..

Ive been asked to look at a rewire, no spec just what I think would be necessary (usually a mid range install, nothing fancy but no ÂŁ1 sockets etc.) Now the install is 40-50 years old and is an overhead supply, as is common to the area the house is in. Looking at the earth coming in it is 2.5mm unsheathed, partially protected by rusty metal capping, and goes out the wall, disappearing under the concrete at the rear of the house, never to be seen again.

I included in my price a new rod, earth pit etc etc. Another electrician has been and told the client that the existing rod is fine and he's tested it blah blah blah (I tested it at 70 ohms). The point isn't that the reading is too high, IMO on a rewire everything needs to be put right ie. the rod needs to be accessible, connections protected etc. and that I'm not happy with the bare minimum size earthing conductor.

That's the moan over with now the question... The client says they want to go ahead with the rewire but keep the existing earth "if it satisfies the regs". Now I know there's a reg that says the connection should be accessible and protected from corrosion in the 17th, but if it was ok to bury them 40 years ago, then can it stay and not conform to the
current edition of regs?
 
Well for starters if the earth is buried where it goes outside it has to be 16mm anyway. So the 2.5 is no good, so if this need replacing then by the time its been traced then the rod may aswel be replaced. Plus although 70 ohms is good, you could get better i reckon
 
Hi chaps, This is part looking for advice, part moan. Bear with me..

Ive been asked to look at a rewire, no spec just what I think would be necessary (usually a mid range install, nothing fancy but no ÂŁ1 sockets etc.) Now the install is 40-50 years old and is an overhead supply, as is common to the area the house is in. Looking at the earth coming in it is 2.5mm unsheathed, partially protected by rusty metal capping, and goes out the wall, disappearing under the concrete at the rear of the house, never to be seen again.

I included in my price a new rod, earth pit etc etc. Another electrician has been and told the client that the existing rod is fine and he's tested it blah blah blah
(I tested it at 70 ohms). The point isn't that the reading is too high, IMO on a rewire everything needs to be put right ie. the rod needs to be accessible, connections protected etc. and that I'm not happy with the bare minimum size earthing conductor.

That's the moan over with now the question... The client says they want to go ahead with the rewire but keep the existing earth "if it satisfies the regs". Now I know there's a reg that says the connection should be accessible and protected from corrosion in the 17th, but if it was ok to bury them 40 years ago, then can it stay and not conform to the
current edition of regs?

Another electrician, isn't, I think you are! :)
 
Well for starters if the earth is buried where it goes outside it has to be 16mm anyway. So the 2.5 is no good, so if this need replacing then by the time its been traced then the rod may aswel be replaced. Plus although 70 ohms is good, you could get better i reckon

Hi David,
If the earth is unsheathed and un-protected, would may be 25mm have to be used ?

Sorry if I'm ahead of myself, TT systems always get me !!

Millboy, as we are currently using the 17th edition of the regs, I would go by them.
I dont know if anyone else agrees?

Sav
 
Hi David,
If the earth is unsheathed and un-protected, would may be 25mm have to be used ?

Sorry if I'm ahead of myself, TT systems always get me !!

Millboy, as we are currently using the 17th edition of the regs, I would go by them.
I dont know if anyone else agrees?

Sav

Sav, you write man,

Cable to the rod need to be 25mm all the way for proper good earth!

Anything less will give you not a strong earth.
 
Sav, you write man,

Cable to the rod need to be 25mm all the way for proper good earth!

Anything less will give you not a strong earth.

16mm, a strong earth you have, skywalker
 
The minimum "Nominal cross-sectional area of earthing lead" was 6mm² in the 14th edition (for live conductors up to 16mm²).


[ElectriciansForums.net] Another bloody TT question
 
Last edited by a moderator:
I'm firmly in the camp of upgrading it lol. I'll have a good look through the book tomorrow and if I can find a few regs to quote I think I can convince them to have it done. To be honest I'm annoyed that they've taken "super duper spark"s opinion over mine anyway.
 

Reply to Another bloody TT question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
436
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top