M

Millboy

Hi chaps, This is part looking for advice, part moan. Bear with me..

Ive been asked to look at a rewire, no spec just what I think would be necessary (usually a mid range install, nothing fancy but no ÂŁ1 sockets etc.) Now the install is 40-50 years old and is an overhead supply, as is common to the area the house is in. Looking at the earth coming in it is 2.5mm unsheathed, partially protected by rusty metal capping, and goes out the wall, disappearing under the concrete at the rear of the house, never to be seen again.

I included in my price a new rod, earth pit etc etc. Another electrician has been and told the client that the existing rod is fine and he's tested it blah blah blah (I tested it at 70 ohms). The point isn't that the reading is too high, IMO on a rewire everything needs to be put right ie. the rod needs to be accessible, connections protected etc. and that I'm not happy with the bare minimum size earthing conductor.

That's the moan over with now the question... The client says they want to go ahead with the rewire but keep the existing earth "if it satisfies the regs". Now I know there's a reg that says the connection should be accessible and protected from corrosion in the 17th, but if it was ok to bury them 40 years ago, then can it stay and not conform to the
current edition of regs?
 
You're assuming that the other sparky will even issue paperwork. Been to a few jobs recently where new CU fitted by "qualified electrician" has no cert with it at all, plus loads of deviations from the regs which are just unacceptable. These cowboys getting more prevalent in the current economic climate it seems....

There's a few round here doing the same, 2 that "know electrics" and have been used for years regardless of what they know and 1 that just took some exams and is now "qualified". None of them can read it seems but they do generate a lot of work for the rest of us.

Anyhow, back to the rod question, sometimes you have to tell the customer what they're getting even if it isn't what they want.
 
As spin notes 2.5mm is acceptable if protected from corrosion and mechanical damage and not buried.

If 2.5 is used then main bonding will only need to be 6mm minimum as well.

6 mm bonding is acceptable right up to 10mm main earth in fact.
 
As spin notes 2.5mm is acceptable if protected from corrosion and mechanical damage and not buried.

If 2.5 is used then main bonding will only need to be 6mm minimum as well.

6 mm bonding is acceptable right up to 10mm main earth in fact.

Good point. However, many TT systems are now being upgraded to PME (I am right now organising one myself) so it is better to install 10mm main bonding.
 
Someone round here just managed to charge a load of people to replace their earth rods. Charged them more than a PME conversion which was available for all the properties. Goes to show that people will believe what bert from the pub tells them.
 
Someone round here just managed to charge a load of people to replace their earth rods. Charged them more than a PME conversion which was available for all the properties. Goes to show that people will believe what bert from the pub tells them.

And probably left them with Ra values of far more, from than what they replaced too!! After all they only need to attain 200ohm at the rod these day's. What's the betting also, that the new rods are all of the thin twig variety!!! .... lol!!
 
I always install 16mm G/Y to rods so if PME is put in later no cable changes are needed. I also don't waste time with 3/8" rods any more. With 5/8" rod and couplers I always get 50 Ohms, or less, at first test.
 

Reply to Another bloody TT question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
436
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top