I've been doing a bit of work on a church which is built on the top of a hill about 300 feet above sea level, the tower is about 100 feet high with open countryside all around.

I have my own theories here but can anyone give me a good reason to connect the lightening conductors, lead in the roof gullies or steelwork in the bell tower (top section of the 100 foot tower) to the MET? None of this metalwork is remotely near any of the electrical system and the 4 lightening conductors run down the outside of the tower to earth.
 
Last edited by a moderator:
I've been doing a bit of work on a church which is built on the top of a hill about 300 feet above sea level, the tower is about 100 feet high with open countryside all around.

I have my own theories here but can anyone give me a good reason to connect the lightening conductors, lead in the roof gullies or steelwork in the bell tower (top section of the 100 foot tower) to the MET? None of this metalwork is remotely near any of the electrical system and the 4 lightening conductors run down the outside of the tower to earth.


As for steelwork in the tower, Potential flash over is the main reason, if open to the elements. (i'm thinking here of steel structure for the church bells) and should be connected to the LP system, not the installations MET. The LP system however should have a link from a down conductor to the MET!!

The bold type above i'm not sure what your saying here, so please explain!! lol!!
 
I've been doing a bit of work on a church which is built on the top of a hill about 300 feet above sea level, the tower is about 100 feet high with open countryside all around.

I have my own theories here but can anyone give me a good reason to connect the lightening conductors, lead in the roof gullies or steelwork in the bell tower (top section of the 100 foot tower) to the MET? None of this metalwork is remotely near any of the electrical system and the 4 lightening conductors run down the outside of the tower to earth.

In a word, regulations, not sure of the reg number, a lightning conductor must be connected to the main earth terminal, everytime I fit one the specialist I employ to fit one insists on it and starts quoting regs, I also get a lecture about fitting surge protection to equipment as well, there must be something in it they keep on about it haha
 
Ok, a couple of reasons for asking. The steel in the bell tower as far as I know (haven't had access way up there yet but it was confirmed on the EICR) is connected to the LP but the LP is not connected to the MET. The company who installed it didn't say anything about needing a connection. The company who re-wired the church didn't connect it, and the company who ran a supply to an out building didn't notice it. The company who did their EICR last year did notice the lack of connections but also noted that there was no connection to the plastic incoming water supply or the lead in the gullies of the roofs. So, here's me, 5th spark on site in as many years and asked to look at the EICR, I took a mate with me today, second pair of eyes and all that. His take on this is that as the LP, lead and metalwork where the bells are (not open to the elements) have no electrical supply, connecting to the MET could introduce a current to somewhere there wouldn't usually be one. Although it's difficult to disagree with the logic, I did start doubting myself.
 
Hi,
Just had a look on the net, English Heritage have a good downloadable PDF entitled 'Lightening protection on Churches'.

May be worth a look,

Regards.
 
Looking at it from a pure physics point of view. A bond should be taken back to the MET from one of the ground spikes. Not from any point above ground and not to all ground spikes.
The reason (as I see it):
Take a point above ground and you will get a voltage gradient which will transfer to the MET and therefore the rest of the electrical system. Regarding the bell frame, either bond it to the LP system or the electrical system, not both.
Link all earth points and the MET becomes a marshalling point for the LP system and the earth bonds are likely to vaporise with the current being transferred.

This is a personal view, and something I’m willing to concede on given good reason. I.E. NOT the reg’s say………..

The reg’s and physics just don’t tally.


Come on E54, you’ve got a target in you’re sights.
[ElectriciansForums.net] Another church question
 
Looking at it from a pure physics point of view. A bond should be taken back to the MET from one of the ground spikes. Not from any point above ground and not to all ground spikes.
The reason (as I see it):
Take a point above ground and you will get a voltage gradient which will transfer to the MET and therefore the rest of the electrical system. Regarding the bell frame, either bond it to the LP system or the electrical system, not both.
Link all earth points and the MET becomes a marshalling point for the LP system and the earth bonds are likely to vaporise with the current being transferred.

This is a personal view, and something I’m willing to concede on given good reason. I.E. NOT the reg’s say………..

The reg’s and physics just don’t tally.


Come on E54, you’ve got a target in you’re sights.

Yes, ...i should of made myself a little clearer when i said down conductor, i was talking about a below ground connection, either at one of the rods, or to a conductor linking the down conductors to the other rod's ... lol!!

I've yet to see a bell tower where the bells are totally enclosed, so they would be open to the elements, ...pretty pointless having bells if they can't be heard over any distance!! So should be connected to the LP system, not the electrical installations MET.

The LP system is bonded to the MET, to decrease the possibilities of lightning flash overs to any earthed/bonded metalwork. These day's any stray lightning currents reaching the buildings electrical system can be protected against by surge protection devices/modules...
 
I've yet to see a bell tower where the bells are totally enclosed, so they would be open to the elements, ...pretty pointless having bells if they can't be heard over any distance!!

All Saints Nottingham. One of T.C. Hines masterpieces. The bells were too loud and the louvers had to be bricked up on the inside.
I lived opposite the bell tower. I couldn't turn the bloody alarm off on a Sunday morning.
 

Reply to Another church question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top