Following on from the last two more technically debated threads:

32A supply for Hot Tub of a PME supply
Another Hot Tub install

I posted a question, in the last one, but didn't get a reply, so starting another one. Hope the Mods don't mind.

So posting my question again, slightly edited.

I’ve been reading lots of threads, about hot tubs & the like, using a PME supply.

I’m thinking of buying one of those inflatable hot tubs Lazy Spa, primarily as a glorified paddling pool for my grandson. I was quite happy to plug into my outdoor socket on my composite (plastic) decking; I have a PME supply.

But since then, I've been reading all sorts things about extending pme (to an outside environment), and I've been contemplating whether to risk it. Manufacturer recommends connecting to equipotential bonding terminal

My options I know, are to either TT just the supply to the tub socket, use my pme supply and try and supplement that with a rod of <20. My sub soil is littered with rocks. Or just use the pme supply without a rod, and don't worry cause its on my plastic decking.

Or just forget it, and keep filling the paddling pool!

Your thoughts?
 
Might it be an idea to put all of them on TT so you don't have to concern yourself about any class 1 stuff plugged in to extension leads, etc, as well?

you cant stop people plugging in extension leads and throwing them in the bath. You cant stop stupidity im affraid! Dont over think it youll go mad otherwise :/
 
With regards to Matt:E I (and others) have been pushing them to give an offical line in the sand in the form of a statement on thier website.

[ElectriciansForums.net] Another Hot Tub Thread Part 2
 
I’ve got other outdoor sockets on pme. I’ve a plan for services, so shouldn’t be hitting anything hopefully.
Also make sure the Rod is not too close to anything metallic in the ground which would be bonded to the PME MET (gas pipes, etc)

As if you are too close to bonded metal work, the voltage from a PEN fault will appear on the earth rod, and you have situation you are trying to mitigate against
[automerge]1598220309[/automerge]
With regards to Matt:E I (and others) have been pushing them to give an offical line in the sand in the form of a statement on thier website.

View attachment 60354
The single phase Matt:e device is not appropriate to protect a hot tub from PEN conductor faults in my opinion, it gives a false sense of security

It is very possible to have a PEN fault where the voltage between L & N remains within 207v - 253v but the voltage between the PEN and true earth are above 70v, this is due to phase imbalances on the network and also extraneous conductive parts within the installations
[automerge]1598220692[/automerge]
Following on from the last two more technically debated threads:

32A supply for Hot Tub of a PME supply
Another Hot Tub install

I posted a question, in the last one, but didn't get a reply, so starting another one. Hope the Mods don't mind.

So posting my question again, slightly edited.

I’ve been reading lots of threads, about hot tubs & the like, using a PME supply.

I’m thinking of buying one of those inflatable hot tubs Lazy Spa, primarily as a glorified paddling pool for my grandson. I was quite happy to plug into my outdoor socket on my composite (plastic) decking; I have a PME supply.

But since then, I've been reading all sorts things about extending pme (to an outside environment), and I've been contemplating whether to risk it. Manufacturer recommends connecting to equipotential bonding terminal

My options I know, are to either TT just the supply to the tub socket, use my pme supply and try and supplement that with a rod of <20. My sub soil is littered with rocks. Or just use the pme supply without a rod, and don't worry cause its on my plastic decking.

Or just forget it, and keep filling the paddling pool!

Your thoughts?
Following on from the last two more technically debated threads:

32A supply for Hot Tub of a PME supply
Another Hot Tub install

I posted a question, in the last one, but didn't get a reply, so starting another one. Hope the Mods don't mind.

So posting my question again, slightly edited.

I’ve been reading lots of threads, about hot tubs & the like, using a PME supply.

I’m thinking of buying one of those inflatable hot tubs Lazy Spa, primarily as a glorified paddling pool for my grandson. I was quite happy to plug into my outdoor socket on my composite (plastic) decking; I have a PME supply.

But since then, I've been reading all sorts things about extending pme (to an outside environment), and I've been contemplating whether to risk it. Manufacturer recommends connecting to equipotential bonding terminal

My options I know, are to either TT just the supply to the tub socket, use my pme supply and try and supplement that with a rod of <20. My sub soil is littered with rocks. Or just use the pme supply without a rod, and don't worry cause its on my plastic decking.

Or just forget it, and keep filling the paddling pool!

Your thoughts?
In the hot weather I looked at how much those Lay-Z-Spas cost, then realised I am short on money from covid plus space to put the thing!

When i was looking into them although, its appeared to me they are class 2 double insulated, I believe the newer models have a heating element sounded in plastic or something like that. So in that case it doesn't matter what the earthing arrangement is as the device doesn't have a connected CPC for any PEN fault voltage to cause a problem.
 
Last edited:
Think I mentioned that I watch a John Ward video (posted June 2020) that he has his doubts about the likes of the Matt:e charger, for the reasons given by @marcuswareham. in fact he suggested the only real fix is item ii of that reg, being a large earth mat under drive or bond to reinforcing bars in foundations, something @davesparks might like to hear.

I have a new build, so all the services are in plastic, so no metal pipes about. The only other issue is neighbours car chargers. One neighbour has an ev, but he’s gone for a podpoint, which is one of those rod less chargers.

Re the Class 2 issue, Lay-z-spa says Class 2 on their web page spec, but Class 1 in the manuals (it also states the pump should be ‘grounded’, lift from US instructions I suppose). I’ve emailed them for clarification.
 
I would go for rod(s) that are fairly close to the hot tub location (within safe and practical fixing, of course), after all the goal is not so much "true Earth" as a low voltage difference to anyone stepping in/out of the tub.
 
37 posts discussing how to fi a plug and play hot tub. the mind is flabbergasted, and on reflection, gets flabbered again.

The manufacturers instructions say to ‘ground’ the pump. I’d rather spend some time getting opinions, before exposing my grandson to any possible dangers. Course I could just not get one.
 
And yet their website clearly states Class II for that very model. Wonder how many of their customers would go to the lengths that you have in order to verify what they might need to do, prior to installing one of these products that are advertised as 'plug and play'.

Very few I suspect.
 
Once you get the hot tub you will know for sure - just a continuity meter's probing away.

So ladies and gentlemen, what do we think the time to thread resurrection will be?
 
Once you get the hot tub you will know for sure - just a continuity meter's probing away.

So ladies and gentlemen, what do we think the time to thread resurrection will be?
I’ll let you know when I’ve put me spike in; won’t be anytime soon though. Mainly because they haven’t any tubs for sale. :)
 
If you haven't bought it yet, you could make sure you buy a class 2 tub and save yourself some work? I've got an Mspa inflatable tub, which is both class 2 and has an inline 10mA RCD.
The manuals I’ve read online, refer to attaching to grounding point etc. No mention of what Class electrical appliance they are? It suggest the pump is 12v.

Yours definitely Class 2.
 

Reply to Another Hot Tub Thread Part 2 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
My girlfriend has a cousin who has lived in Japan for at least 15 years teaching English yet he can barely speak their language.
    • Like
    • Informative
Replies
4
Views
360

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top