So next week I have to add a circuit to this board:

[ElectriciansForums.net] Anyone go the BBB to hand - reg regarding mix and match


My plan is to add a Wylex breaker ........... but how would the BBB wording cover this?

I haven't bough the BBB yet!

After all, its not me that added the 3rd party breakers:):):):):)
 
No, and I never suggested you should not use the tools you currently have.
I am just pointing out that we all need to be aware of the accuracy and tolerance of the test equipment we use.

loop impedance tests can have quite a high tolerance at low values.
I always remember testing Zs at a block for students, new build our company did, using a kewtech kt64 my colleague recorded 0.00 ohms, block was about 30 meters away and the cable was 120mm2 4 core swa with separate 70mm cpc.
My megger 1552 recorded 0.04 ohms and at the main distribution panel a ZE of 0.01 ohms which rallied up with the DNO design figure.
So I do realise the tolerance levels of different manufacturers testing equipment.
Just an example of 2 meters with different outcomes.
 
No, and I never suggested you should not use the tools you currently have.
I am just pointing out that we all need to be aware of the accuracy and tolerance of the test equipment we use.

loop impedance tests can have quite a high tolerance at low values.
I always remember testing Zs at a block for students, new build our company did, using a kewtech kt64 my colleague recorded 0.00 ohms, block was about 30 meters away and the cable was 120mm2 4 core swa with separate 70mm cpc.
My megger 1552 recorded 0.05 ohms (zs)and at the main distribution panel a ZE of 0.01 ohms which tallied up with the DNO design figure.
So I do realise the tolerance levels of different manufacturers testing equipment.
Just an example of 2 mft meters with different outcomes at low values.
Again it’s as accurate as I could get with the equipment used.
 
I always remember testing Zs at a block for students, new build our company did, using a kewtech kt64 my colleague recorded 0.00 ohms, block was about 30 meters away and the cable was 120mm2 4 core swa with separate 70mm cpc.
My megger 1552 recorded 0.05 ohms (zs)and at the main distribution panel a ZE of 0.01 ohms which tallied up with the DNO design figure.
So I do realise the tolerance levels of different manufacturers testing equipment.
Just an example of 2 mft meters with different outcomes at low values.
Again it’s as accurate as I could get with the equipment used.
What was the measured PFC?
 
What was the measured PFC?
Where at the origin or the block?
Origin was about 46ka. Measured between line and neutral then doubled as the meter couldn’t read higher than 19ka between lines.
It was 3 years ago but something like that.
2x 400mm singles in parallel connecting from the ACB at the transformer and a 400mm earthing conductor
 
Last edited:
Right, regs is regs so I will not mix and match CU components.

The reasoning being from the pocket lining barstewards manufacturers is we haven't tested so we wont take responsibility for the installation being safe.

My question is, if you arrive at a CU with preexisting mixed components can you carry out works on it?
 
Right, regs is regs so I will not mix and match CU components.

The reasoning being from the pocket lining barstewards manufacturers is we haven't tested so we wont take responsibility for the installation being safe.

My question is, if you arrive at a CU with preexisting mixed components can you carry out works on it?
Don't think it actually says that you can't mix devices, there are procedures to follow if you do need to mix and match.
 
funny that. just quoted a job to fit a new shower. 1960'shager DB, no RCD, and the ptatt who fitted the existing shower ( 9.5kW wired in 10.0mm ) fitted a 50A Volex MCB on it. this was under 3 years ago, so apart from mixing devices, he'd completely ignored the fact that he should have fitted a RCBO.
 
Don't think it actually says that you can't mix devices, there are procedures to follow if you do need to mix and match.

Yes it does, short of taking on design responsibilities for the enclosure and components. I can't believe there are that many sparks who are qualified and experienced enough to take that responsibility on.
 
think what pete means is that if you get confirmation from,say, wylex, that hager MCBs can be mixed in a wylex board, you're good to go.
 
This prohibition started in domestic installations with AMD3. CUs must comply with BS EN 61439-3.
This requirement prevents the use of DBs intended for non-domestic use and effectively prohibits mixing and matching, as the type testing would be invalidated.
All this new requirement does is extend the prohibition to non-domestic DBs.
 

Reply to Anyone go the BBB to hand - reg regarding mix and match in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
857