Hi All

Just wondering how you guys approach requests for downlight installs. Upto now I only attempt them if have access to floor boards above or the ceiling has been temporarily dropped so have easy wiring access. If ceiling is the more modern suspended type ceiling obviously not a problem to wire them. But how do you access this to the point you feel comfortable going ahead with it. Concern is take on a job that appears to be suspended and has ease of wiring start chopping away for downlight holes and then find there's either wooden supports or some sort of hindrance for the wiring
 
Hi All

Just wondering how you guys approach requests for downlight installs. Upto now I only attempt them if have access to floor boards above or the ceiling has been temporarily dropped so have easy wiring access. If ceiling is the more modern suspended type ceiling obviously not a problem to wire them. But how do you access this to the point you feel comfortable going ahead with it. Concern is take on a job that appears to be suspended and has ease of wiring start chopping away for downlight holes and then find there's either wooden supports or some sort of hindrance for the wiring
Admittedly this answer is now more for current people searching for this area, but I hope this helps.

This is exactly what I do, other people can and will have different methods. This is not used when acess above is an open accessible loft etc. This is floors with rooms above and when all building elements are fully finished, details on required regs and suitable materials are not included here, this is how I treat my potential customers re downlight install pre quotes only.

There are a few basic steps and a load of precautions I take first, I make all these clear to the customer first before any further steps like choosing the lights take place (and waaay before quoting) and if there is any doubt from either party, I simply offer an hourly rate and walk if not suitable, hourly rate is the backup and last resort and it allows you safety from loss, I also explain this to the customer.

You must visit the property to assess before any of this can be done....

Basic steps and precautions:
1 it's either ceilings down or floors up, no other option, just a matter of damage limitation which you make them financially aware of (they will need to source and pay plasterers etc). Check they are ok with this.
2 mess, there will be managed but sustained mess throughout, are they ok with this?
3 asbestos, likely if the property is older than the eighties and possible for early nineties, discuss this, learn about this for yourself, usually lower amounts (if any) within newer property, I make them aware that it might be there... And discuss a solution that suits both sides and current law/safety.
4 original cables and pipes - massive hazard, this will need to be assessed EVERY cut, for ceilings, beams and floors:

Floor cutting - accurate depth set skilsaw to avoid hidden cables and pipes.
Ceiling cutting - jabsaw, holesaw dust cowl.
Beams - augur, flat bit etc

5 rare but possible, the unknown... There may be a deviation from and quote once we see what we are dealing with hidden within the floor void, and in very rare cases, damage to other systems, I advise that every possible effort will be made by myself to avoid this, but accidents can happen, and if you look carefully, legally, as long as you show due care, you are not responsible for subsequent damage (look this up, it is very important). Make them aware of ALL this, they still want downlights?....

6 locations are dictated to by beams, so there will have to be compromise on placement to some degree.

7 are they good to accept ALL items? Check this repeatedly while there assessing.

8 put it ALL in writing with quote.

Aaaaand that's it?

I totally use this method to do two things: firstly to ensure we're all clear on how complicated this can be for ALL involved and secondly to weed out those who saw it at their friends in their new kitchen/extension/house etc and thought it'd be a nice affordable upgrade....

Treat this kind of thing as a serious installation and don't go in cheap ever, it'll save you hassle in the long run.

Cheers???
 
slight tangent but.... we have prescribed zones in walls in line with accessories, right? so why not prescribed zones in ceilings in line with the downlights? then we could just chip out round the bottom of the joists, clip cable to underside of joists, fish over to next joist, and just minimal patching. have to admit to doing this a couple of times even though it's not strictly compliant. any thoughts?
 
I have never seen doing this as a particularly big issue even thou it goes against the spirit of the 50mm clearance for nails or screws.

Its similar to when you are in a real bind to opting to put a cable behind a skirting board, I don’t like it but can See why some sparks do it.

We don’t live in a perfect world where every job can be perfect and quite often customers don’t want all their ceilings and walls mashed up just to get an extra cable in...
 
slight tangent but.... we have prescribed zones in walls in line with accessories, right? so why not prescribed zones in ceilings in line with the downlights? then we could just chip out round the bottom of the joists, clip cable to underside of joists, fish over to next joist, and just minimal patching. have to admit to doing this a couple of times even though it's not strictly compliant. any thoughts?
Gotta be honest for me this is about as DIY as it gets and I'd never do it. Just dont think its professional. Not a criticism just a personal opinion.
My approach is as follows and as per post #17 all potential pitfalls are discussed with client at quote stage.
I cut traps about 200mm square with a jabsaw between joists (located by tapping ceiling!) and use a right angle drill to go through joists. Hand tools for cutting reduce the risk to cables and pipes in the void because with care you can 'feel' something before its too late.
Once wiring is complete a couple of bits of batten are passed up through the holes and fixed through the plasterboard, and then the same bit of plasterboard that was cut out is put back in its hole and fixed to the batten. If the client wants me to I will make good to a standard which will be almost invisible one painted, but this may require a return visit. I normally use multi finish which goes off quickly and then skim a fine layer of powder mix filler over. A day or so later come back and lightly rub down. Even on finely finished ceilings clients have always been surprised at the final result once they've re decorated. Pretty much invisible.
 
Radiohead , in a perfect world yours would be the best practice.

But loads of houses I seem to get called to have artex / stippled or lath and plaster ceilings. Cutting big hatches and trying to patch plaster the following day takes ages and customers often very reluctant to pay for the extra time.

A little notch under each joist to clip a bit of 1mm to the underside creates far less distruction and can be back filled with poly filler and repainted that same afternoon
 
slight tangent but.... we have prescribed zones in walls in line with accessories, right? so why not prescribed zones in ceilings in line with the downlights? then we could just chip out round the bottom of the joists, clip cable to underside of joists, fish over to next joist, and just minimal patching. have to admit to doing this a couple of times even though it's not strictly compliant. any thoughts?
I've been meaning to buy a roll of BS 8436 cable for such occasions. Can do this and remain compliant.
 
which brings me back to my post... why not nominate in line with lights as safe zones similar to walls? the method would then comply.

cost being a factor, it's way less expensive than cutting and repairing huge holes, and eliminates the risk of drilling blind through joists, trying to miss any cables etc.that can't be seen.

apart from which, it's farless likely to be screwed or nailed than a cable in a wall.not many customers want to hang pictures or fit shelves on a ceiling.
 
I just cut a 100mm strip up centre of the room, and the odd cut for noggins, use screwdriver to poke 35mm eitherside of centre of spot.
Patch, then they get there own plaster.

Keep any holes u cut away from spotlight positions.. Finished the same day
 
As above really, I'll almost always cut holes either side of the joist to make sure I don't find services with my drill bit. I also have a ferret inspection camera that has paid for itself many times over for this kind of thing.

A bit of imagination with cable routing goes a long way too.

As long as the customer is aware of the possible worst case scenario then all is good.

I'll patch the plasterboard but not fill afterwards, I leave that to a decorator or plasterer.

The only time I won't go near it is if it's a lath and plaster ceiling.
Yh can be messy and dusty
 
slight tangent but.... we have prescribed zones in walls in line with accessories, right? so why not prescribed zones in ceilings in line with the downlights? then we could just chip out round the bottom of the joists, clip cable to underside of joists, fish over to next joist, and just minimal patching. have to admit to doing this a couple of times even though it's not strictly compliant. any thoughts?
When working there are more than Electrical regulations to consider. Now you are into a very separate set of operational parameters, building regulations, regulations for beams mean they have very strict allowances for width, depth and location of 'chipping out' or drilling holes, hence why it must not be done unless within said allowances (don't take my word for it look up the specifics), same as location of holes size and proximity etc. A structural beam providing support over an unsupported span is vulnerable to alterations outside of 'safe' zones causing weakness in relation to the location, loads, span and size of beam. This is why I personally never 'chip' out of the top or base of a beam, and instead factor it into the pricing and time, in my opinion it's not acceptable where one should be pricing to cover completing within full regulations. As I said earlier, my point 5 rare but possible, the unknown... The trick is to learn your materials/building fabrics and how long it takes you to achieve what your customer wants-remember to walk away, if you aren't able to do it in the budget they have them don't. Just how I work ??
 
When working there are more than Electrical regulations to consider. Now you are into a very separate set of operational parameters, building regulations, regulations for beams mean they have very strict allowances for width, depth and location of 'chipping out' or drilling holes, hence why it must not be done unless within said allowances (don't take my word for it look up the specifics), same as location of holes size and proximity etc. A structural beam providing support over an unsupported span is vulnerable to alterations outside of 'safe' zones causing weakness in relation to the location, loads, span and size of beam. This is why I personally never 'chip' out of the top or base of a beam, and instead factor it into the pricing and time, in my opinion it's not acceptable where one should be pricing to cover completing within full regulations. As I said earlier, my point 5 rare but possible, the unknown... The trick is to learn your materials/building fabrics and how long it takes you to achieve what your customer wants-remember to walk away, if you aren't able to do it in the budget they have them don't. Just how I work ??
my suggested method does not cut into the joists at all. just into the ceiling board. then cable/s clipped to the bottom of the joist/s.
 

Reply to Approach for downlight install requests in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
885
  • Article
Electrical2Go - Home Security: Using Floodlights, CCTV, and Door Entry Systems In an era where technology is advancing rapidly, home security has...
Replies
0
Views
991

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top