in LVE , SPD is before main switch View attachment 54817



[automerge]1577093974[/automerge]

In the LVE board it’s before main switch, I’m trying to understand this and the way it’s wired, it appears to be wired before the main switch aswell.View attachment 54818
In that style of board the SPD is after the main switch. The meter tails terminate into the top of the main switch.

Ideally on an installation all consumer equipment should be after a main switch to allow for safe isolation. But if the supply was split before the main switch then the SPD would have to be before the switch as it is designed to protect the installation and not just the board..

With a lot of manufacturers if the main installation supply fuse (DNO) is below a certain rating there's no requirement for over-current protection for the SPD.
 
Refering to your LVE board , The incomming tails would terminate into the top of the main switch, so the SPD would be after the main switch.
Sorry I’ve looking at this in the wrong way , the SPD is after the main switch and is pre wired , no need for over current protection , think I’ve got that now
[automerge]1577099221[/automerge]
In that style of board the SPD is after the main switch. The meter tails terminate into the top of the main switch.

Ideally on an installation all consumer equipment should be after a main switch to allow for safe isolation. But if the supply was split before the main switch then the SPD would have to be before the switch as it is designed to protect the installation and not just the board..

With a lot of manufacturers if the main installation supply fuse (DNO) is below a certain rating there's no requirement for over-current protection for the SPD.
When SPD is after main switch and is pre wired , then the is no current flowing through it , am I correct .
 
Sorry I’ve looking at this in the wrong way , the SPD is after the main switch and is pre wired , no need for over current protection , think I’ve got that now
[automerge]1577099221[/automerge]

When SPD is after main switch and is pre wired , then the is no current flowing through it , am I correct .

Whether it needs over current protection is down to the manufacturer.

SPDs are typically metal oxide varistors... At mains voltage these are high resistance and consequently pass no to little current. As the voltage increases, there resistance drops and they conduct more current, dumping the spikes to earth. They may also has discharge arrestors (I think that's what they are called).

The same technology is present in surge arresting extensions which can cause low insulation resistance readings (tip... If an IR test is poor at 500v, if it's good at 250v, it's possibly a surge arrester in circuit).
 
In normal circumstances there is no current flowing through them. They only become active if transient voltages occur diverting them to earth before it can cause possible damage to equipment. In your pic an earth is required from the device to the consumer unit earth terminal.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Are surge protection devices fitted before or after the main switch
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
L1Jay1,
Last reply from
Mike Johnson,
Replies
30
Views
12,074

Advert

TrueNAS JBOD Storage Server

Back
Top