in LVE , SPD is before main switch View attachment 54817



[automerge]1577093974[/automerge]

In the LVE board it’s before main switch, I’m trying to understand this and the way it’s wired, it appears to be wired before the main switch aswell.View attachment 54818
In that style of board the SPD is after the main switch. The meter tails terminate into the top of the main switch.

Ideally on an installation all consumer equipment should be after a main switch to allow for safe isolation. But if the supply was split before the main switch then the SPD would have to be before the switch as it is designed to protect the installation and not just the board..

With a lot of manufacturers if the main installation supply fuse (DNO) is below a certain rating there's no requirement for over-current protection for the SPD.
 
Refering to your LVE board , The incomming tails would terminate into the top of the main switch, so the SPD would be after the main switch.
Sorry I’ve looking at this in the wrong way , the SPD is after the main switch and is pre wired , no need for over current protection , think I’ve got that now
[automerge]1577099221[/automerge]
In that style of board the SPD is after the main switch. The meter tails terminate into the top of the main switch.

Ideally on an installation all consumer equipment should be after a main switch to allow for safe isolation. But if the supply was split before the main switch then the SPD would have to be before the switch as it is designed to protect the installation and not just the board..

With a lot of manufacturers if the main installation supply fuse (DNO) is below a certain rating there's no requirement for over-current protection for the SPD.
When SPD is after main switch and is pre wired , then the is no current flowing through it , am I correct .
 
Sorry I’ve looking at this in the wrong way , the SPD is after the main switch and is pre wired , no need for over current protection , think I’ve got that now
[automerge]1577099221[/automerge]

When SPD is after main switch and is pre wired , then the is no current flowing through it , am I correct .

Whether it needs over current protection is down to the manufacturer.

SPDs are typically metal oxide varistors... At mains voltage these are high resistance and consequently pass no to little current. As the voltage increases, there resistance drops and they conduct more current, dumping the spikes to earth. They may also has discharge arrestors (I think that's what they are called).

The same technology is present in surge arresting extensions which can cause low insulation resistance readings (tip... If an IR test is poor at 500v, if it's good at 250v, it's possibly a surge arrester in circuit).
 
In normal circumstances there is no current flowing through them. They only become active if transient voltages occur diverting them to earth before it can cause possible damage to equipment. In your pic an earth is required from the device to the consumer unit earth terminal.
 
Ian 1981 is correct, the devices are after the outgoing terminals of the main switch, in parallel with the busbar. You can see the neutral looped from the outgoing terminal.
 

Reply to Are surge protection devices fitted before or after the main switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
1K
You can get surge-protected 13A plugs such as this...
Replies
2
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top