How about you guys take a look at his profile and maybe go a little easier on him... it clearly states he's a trainee... just because someone doesn't have the trainee tag, doesn't mean they aren't.

@L1Jay1 , maybe consider signing up for the trainee section of the forums. You'll get a trainee tag so everyone can see you're training and you'll get access to a trainee only area which only trainees, staff and mentors can access so you can ask questions such as this without getting this kind of response.

To answer your question, they would generally be installed after the main switch. The ones in most domestic boards are installed as close to the main switch as possible, many are supplied via a circuit breaker (I've seen 32A for all the ones I've seen) but some, Hager I think, are connected straight to the main switch itself. But as @Strima says... what do the manufacturers instructions say?
 
Have a think about what the main switch does, and what it is for.
if you don’t know the answer, then maybe someone competent should be doing the work.
I’m simply asking the question
[automerge]1577085576[/automerge]
Clearly 'tis the season to be grumpy!

How about you guys take a look at his profile and maybe go a little easier on him... it clearly states he's a trainee... just because someone doesn't have the trainee tag, doesn't mean they aren't.

@L1Jay1 , maybe consider signing up for the trainee section of the forums. You'll get a trainee tag so everyone can see you're training and you'll get access to a trainee only area which only trainees, staff and mentors can access so you can ask questions such as this without getting this kind of response.

To answer your question, they would generally be installed after the main switch. The ones in most domestic boards are installed as close to the main switch as possible, many are supplied via a circuit breaker (I've seen 32A for all the ones I've seen) but some, Hager I think, are connected straight to the main switch itself. But as @Strima says... what do the manufacturers instructions say?
In the live boards the spd is before the main switch
[automerge]1577085641[/automerge]
What about putting it in the closet ?
What about putting you in the closet
 
Hi - normally the main switch isolates all the equipment in the board, is that what you mean? :)
Sorry I meant a LVE board , I’ve seen a LVE board with surge protection already installed in it , the SPD is before the main switch in this board , this got me confused.
[automerge]1577089291[/automerge]
Clearly 'tis the season to be grumpy!

How about you guys take a look at his profile and maybe go a little easier on him... it clearly states he's a trainee... just because someone doesn't have the trainee tag, doesn't mean they aren't.

@L1Jay1 , maybe consider signing up for the trainee section of the forums. You'll get a trainee tag so everyone can see you're training and you'll get access to a trainee only area which only trainees, staff and mentors can access so you can ask questions such as this without getting this kind of response.

To answer your question, they would generally be installed after the main switch. The ones in most domestic boards are installed as close to the main switch as possible, many are supplied via a circuit breaker (I've seen 32A for all the ones I've seen) but some, Hager I think, are connected straight to the main switch itself. But as @Strima says... what do the manufacturers instructions say?
Sorry I meant LVE board , not live
 
Sorry I meant a LVE board , I’ve seen a LVE board with surge protection already installed in it , the SPD is before the main switch in this board , this got me confused.

[ElectriciansForums.net] Are surge protection devices fitted before or after the main switch


This picture illustrates @DPG 's point perfectly. Physically it appears before if you're looking from right to left, but wiring wise it's most definitely after the main switch.
 
I was trying to think of a way of wording that @DPG, stupid hangover! ?

I was trying to think of a way of wording that @DPG, stupid hangover! ?
When you say the SPD is before the main switch, do you mean physical position or actual wiring order though?

I was trying to think of a way of wording that @DPG, stupid hangover! ?

View attachment 54815

This picture illustrates @DPG 's point perfectly. Physically it appears before if you're looking from right to left, but wiring wise it's most definitely after the main switch.
View attachment 54815

This picture illustrates @DPG 's point perfectly. Physically it appears before if you're looking from right to left, but wiring wise it's most definitely after the main switch.
View attachment 54815

This picture illustrates @DPG 's point perfectly. Physically it appears before if you're looking from right to left, but wiring wise it's most definitely after the main switch.
Clearly 'tis the season to be grumpy!

How about you guys take a look at his profile and maybe go a little easier on him... it clearly states he's a trainee... just because someone doesn't have the trainee tag, doesn't mean they aren't.

@L1Jay1 , maybe consider signing up for the trainee section of the forums. You'll get a trainee tag so everyone can see you're training and you'll get access to a trainee only area which only trainees, staff and mentors can access so you can ask questions such as this without getting this kind of response.

To answer your question, they would generally be installed after the main switch. The ones in most domestic boards are installed as close to the main switch as possible, many are supplied via a circuit breaker (I've seen 32A for all the ones I've seen) but some, Hager I think, are connected straight to the main switch itself. But as @Strima says... what do the manufacturers instructions say?
When you say the SPD is before the main switch, do you mean physical position or actual wiring order though?
When you say the SPD is before the main switch, do you mean physical position or actual wiring order though?
in LVE , SPD is before main switch
[ElectriciansForums.net] Are surge protection devices fitted before or after the main switch


Have a think about what the main switch does, and what it is for.
if you don’t know the answer, then maybe someone competent should be doing the work.
When you say the SPD is before the main switch, do you mean physical position or actual wiring order though?
[automerge]1577093974[/automerge]
View attachment 54815

This picture illustrates @DPG 's point perfectly. Physically it appears before if you're looking from right to left, but wiring wise it's most definitely after the main switch.
In the LVE board it’s before main switch, I’m trying to understand this and the way it’s wired, it appears to be wired before the main switch aswell.
[ElectriciansForums.net] Are surge protection devices fitted before or after the main switch
 

Reply to Are surge protection devices fitted before or after the main switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
1K
You can get surge-protected 13A plugs such as this...
Replies
2
Views
387