I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

What would your rcd do if you decided to prod at line and neutral?
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

What would your rcd do if you decided to prod at line and neutral?
 
I know it's not true but based on that reg alone it states :

Basic Protection
Persons and livestock shall be protected against dangers that may arise from contact with live parts of the installation.

This protection can be achieved by one of the following methods:

  1. Preventing a current passing through the body of any person or any livestock
  2. Limiting the current which can pass through a body to a non-hazardous valve
Now taking that to the letter without referring to any other regulation an RCD does exactly that, this is a very poorly written regulation and would afford you great defence in court.

What would your rcd do if you decided to prod at line and neutral?
 
Why do we have a 30ma RCD if the result is a pass through of a massive current, it would make a mockery of it
It means that it will operate if there is a nominal 30mA earth fault current through it (between 0.5 and 1 times this in reality). So if you were in contact with a phase conductor and 30mA passed through your body it should operate. The 30mA rating has nothing to do with limiting the fault current to 30mA as this would defy Ohm's Law.
 
I see so what's the point of that level, 30mA
To protect human life.

It's not about limiting the current to 30mA but ensuring that it operates if 30mA is passing through - well actually 150mA for additional protection to operate within 40mS.
 
To protect human life.

It's not about limiting the current to 30mA but ensuring that it operates if 30mA is passing through - well actually 150mA for additional protection to operate within 40mS.
But if the result is an instant huge fault current that starts way above that figure why have it, hence my argument that the fault current grows from zero and fast.. In milliseconds; but is nipped in the bud by the RCD before it gets the chance. Plus if your argument is true why doesn't a 500mA protect you.
 
Last edited:

Reply to Automatic disconnection of supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top