5 single phases to one huge property.
Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through the 2 pole ats which has been pre installed with the earths linking through to the pme system ( think for a 32a backup generator ) and then the other phase has a 2 pole manual transfer switch with a commando socket rated to 63a but it’s a 30-40m run so you could potentially use another phase which feeds 2 db’s
I’m sure you can limit things on the generator to control distribution of power and how much but haven’t got to that yet.
Generator also has a 100ma rcbo and 2 main sw’s installed
Earthing arrangements : 5 separate pme supplies sharing neutral and earth.
Generator speced to have an earth rod installed.
Thinking about TT’n the whole lot and making an island while keeping the pme separate. and as I dont want different potentials from generators tt earth
What’s everyone’s opinions is that my safest route or can I connect the pme to a 106 amp generator? Wouldn’t want someone on the cable fixing it and getting a whack since there’s a path to earth if connected onto pme
Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through the 2 pole ats which has been pre installed with the earths linking through to the pme system ( think for a 32a backup generator ) and then the other phase has a 2 pole manual transfer switch with a commando socket rated to 63a but it’s a 30-40m run so you could potentially use another phase which feeds 2 db’s
I’m sure you can limit things on the generator to control distribution of power and how much but haven’t got to that yet.
Generator also has a 100ma rcbo and 2 main sw’s installed
Earthing arrangements : 5 separate pme supplies sharing neutral and earth.
Generator speced to have an earth rod installed.
Thinking about TT’n the whole lot and making an island while keeping the pme separate. and as I dont want different potentials from generators tt earth
What’s everyone’s opinions is that my safest route or can I connect the pme to a 106 amp generator? Wouldn’t want someone on the cable fixing it and getting a whack since there’s a path to earth if connected onto pme