Backup 106A generator earthing arrangement questions | on ElectriciansForums

Discuss Backup 106A generator earthing arrangement questions in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 14, 2022
Messages
1
Reaction score
0
Location
kendal
5 single phases to one huge property.



Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through the 2 pole ats which has been pre installed with the earths linking through to the pme system ( think for a 32a backup generator ) and then the other phase has a 2 pole manual transfer switch with a commando socket rated to 63a but it’s a 30-40m run so you could potentially use another phase which feeds 2 db’s



I’m sure you can limit things on the generator to control distribution of power and how much but haven’t got to that yet.



Generator also has a 100ma rcbo and 2 main sw’s installed



Earthing arrangements : 5 separate pme supplies sharing neutral and earth.



Generator speced to have an earth rod installed.



Thinking about TT’n the whole lot and making an island while keeping the pme separate. and as I dont want different potentials from generators tt earth



What’s everyone’s opinions is that my safest route or can I connect the pme to a 106 amp generator? Wouldn’t want someone on the cable fixing it and getting a whack since there’s a path to earth if connected onto pme
 
Generators of that size are normally TN supplies as N & E is linked within the generator, the fact you have an earth rod is not making it TT.

You do need the rod as an independent means of earthing since during loss of supply conditions you cannot assume the supply earth is present.

Since you are not allowed to link N-E at more than one point, and the main supply is already linked at the substation (either low impedance if TN/PME, or via substation Earth if TT), then all arrangements to switch power must switch both L1-L3 (as used) & N to preserve only one N-E link at a time. Those transfer switches should prevent any risk of back-driving the supply.

Where you might want to TT the arrangement is for safety as under loss of supply / out-of-specification supply it could be due to an open PEN fault and under those conditions the generator could be at an elevated potential w.r.t. true Earth so a risk for anyone working on it, such as checking operation or stopping/refuelling/starting, etc.
 
Not sure I'm fully understanding what the question is, here. Generator supply will be TN-S, the generator requires an earth rod for referencing (BS7430), and your changeover switching (auto or manual) also requires isolation of the [DNO] supply earth.
 
5 single phases to one huge property.



Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through the 2 pole ats which has been pre installed with the earths linking through to the pme system ( think for a 32a backup generator ) and then the other phase has a 2 pole manual transfer switch with a commando socket rated to 63a but it’s a 30-40m run so you could potentially use another phase which feeds 2 db’s



I’m sure you can limit things on the generator to control distribution of power and how much but haven’t got to that yet.



Generator also has a 100ma rcbo and 2 main sw’s installed



Earthing arrangements : 5 separate pme supplies sharing neutral and earth.



Generator speced to have an earth rod installed.



Thinking about TT’n the whole lot and making an island while keeping the pme separate. and as I dont want different potentials from generators tt earth



What’s everyone’s opinions is that my safest route or can I connect the pme to a 106 amp generator? Wouldn’t want someone on the cable fixing it and getting a whack since there’s a path to earth if connected onto pme
Maybe I am struggling a bit here but what is the question?
 
5 single phases to one huge property.



Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through the 2 pole ats which has been pre installed with the earths linking through to the pme system ( think for a 32a backup generator ) and then the other phase has a 2 pole manual transfer switch with a commando socket rated to 63a but it’s a 30-40m run so you could potentially use another phase which feeds 2 db’s



I’m sure you can limit things on the generator to control distribution of power and how much but haven’t got to that yet.



Generator also has a 100ma rcbo and 2 main sw’s installed



Earthing arrangements : 5 separate pme supplies sharing neutral and earth.



Generator speced to have an earth rod installed.



Thinking about TT’n the whole lot and making an island while keeping the pme separate. and as I dont want different potentials from generators tt earth



What’s everyone’s opinions is that my safest route or can I connect the pme to a 106 amp generator? Wouldn’t want someone on the cable fixing it and getting a whack since there’s a path to earth if connected onto pme
is this on a changeover switch and a diesel engine for example? so when the power in a building goes off a Lovato/ automatic system kicks it in, or is it just a back up manual genny on a farm or a large domestic premisis. You said manual switch, how?
 
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will automatically disconnect the supply if there is an issue.

For this to work properly, you need to be in 'island' mode with a generator switch over point breaking all contact with the grid.

I'm not fantastic with the science but enough SME people told me either the grid is in charge or the generator, no power sharing deal to be had.

For info, I spent a decade designing, building, and maintaining sites running with multiple generators up to 720kva each in parallel with sites covering several sqkm. This use to be quite a manual task running in parallel using filament bulbs to match supplies from multiple generators using potentiometers, thank god for the digital age and button pushing 😂
 

Reply to Backup 106A generator earthing arrangement questions in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top