After numerous jobs having to go along and rectify very sub standard work its started to get me thinking. The more common things i come across is poor labelling at dist boards, Cables not sized right, inadequate protection jobs half finished. I recently came across a 13amp double socket wired in 1.5mm T&E protected by 63amp HRC fuse. I also came across an immersion heater with live and neutral both connected together missing the elements. I know some plumbers etc try there hand but its not in every case.
I`m just curious as to what the worst scenario anyone else has come across.
went to a new build extension last year the guy that wired it was "approved" apparently.
downstairs toilet light wasn't working and he wouldn't come back to sort it.
this was a massive extension with open plan kitchen and upstair master bedroom and ensuite bathroom.
nice people owned the place got totally stiffed on the price.
ask for test certs and got handed a home made sheet labeled "small works order" with no sign of any test results.
pulled down toilet light to find a link between earth and neutral ,on splitting link and quick test no neutral at the light ,tncs system in property scary.
was asked to test the whole extension this is what i found:
whole extension had been spliced into the exising building using JBs
fuse board old wylex on rewireables was feeding extension
all the light including about 20 halogens in the kitchen ,none fire rated, were on a 16amp wireable which also fed some downstairs sockets in the existing property.
extension ring main had been grafted onto a radial which was on a 32a rewirable.
no ip rated downlighters in shower cubicle
no earth bonding at all
nothing marked obviously.
finally no RCD's on anything
turned out to be the job from hell and it cost them a lot of money to put right.
in this area building regs are a joke no one from building control is checking up on finished work being up to spec or signed off,make's me wonder why we bother.
turns out a call to the local building inspectors revelled they have no one qualified to make such checks.
so much for Part "P"
quality
elfyn