Hi all,

I need to supply an outdoor barbeque area with sockets and lights. (10m away from house)

Running a distribution circuit from the cu in house will be extremly difficult due to location.

The system is Tncs. House is 10 year old.

Im thinking of spuring off a socket on the downstairs ring main to supply a db at the barbeque area, not connecting the earth at the barbeque end but knock a rod in for the outdoor db.

Id like your thoughts please.

Thanks
 
Well subject to loading on the existing RFC you could possibly come off with a 4mm 3 core SWA to a small DB as a means of connecting the power and lighting, MCBs could be rated at 16 and 6 amps respectively. OP - why do you think you need to create a TT earthing arrangement for the barbeque area ?
 
Well subject to loading on the existing RFC you could possibly come off with a 4mm 3 core SWA to a small DB as a means of connecting the power and lighting, MCBs could be rated at 16 and 6 amps respectively. OP - why do you think you need to create a TT earthing arrangement for the barbeque area ?

Thats my intention Dave, the the tt system outdoors would be for the prevention off exporting the earth on a tncs.
 
Thats my intention Dave, the the tt system outdoors would be for the prevention off exporting the earth on a tncs.
CRAP. you'd only consider a TT if the outdoor installation was in a metal building or a caravan, maybe for reasons of bonding extraneous parts, ( excepting some agricultural situations, which do not apply here ).
 
If you worried about exporting/extending PME, whatever the terminology the masses what to use, goggle it. Lots of advice in pdf format. Are you in a scheme? What do they advise?
 

Reply to Barbeque area supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
548
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top