Found this on a large testing companies website:
'Where the mains supply is connected, as will be the case for periodic testing, the protective and equipotential conductors must not be disconnected because if a fault occurs these conductors may rise to a high potential above earth. In this case, an earth-fault loop tester can be used to verify the integrity of the protective system.'
So wrong, I wonder how many wrongly measured Ze readings they've reported (parallel paths). I emailed them suggesting they might consider turning of the main isolator to reduce the risk of the conductors rising to 'a high potential above earth' before disconnecting the main earth for a real Ze test..
Big company as well..
Ride em cowboy!
'Where the mains supply is connected, as will be the case for periodic testing, the protective and equipotential conductors must not be disconnected because if a fault occurs these conductors may rise to a high potential above earth. In this case, an earth-fault loop tester can be used to verify the integrity of the protective system.'
So wrong, I wonder how many wrongly measured Ze readings they've reported (parallel paths). I emailed them suggesting they might consider turning of the main isolator to reduce the risk of the conductors rising to 'a high potential above earth' before disconnecting the main earth for a real Ze test..