How would you be able to ascertain the value of the supply earth (Ze) if you can't isolate it from protective bonding?
To be frank I don't very often come across situations where I can't isolate the supply and carry out a Ze loop test and check continuity of the protective conductors. The situation I illustrated, a malfunction clamp, is a real situation which would not have shown up with a zs loop test with all protective conductors connected because of parallel paths... Where's my bad practice?
cheers
s
any one ever done ze with earth connected and then retested when disconected never much in the readings and sometimes the same reading anyone had same issues
HOW do you Issolate the supply fully? If its by removing DNO fuse then you are acting Illegaly and by recording this on cert you are admitting your guiltTo be frank I don't very often come across situations where I can't isolate the supply and carry out a Ze loop test and check continuity of the protective conductors. The situation I illustrated, a malfunction clamp, is a real situation which would not have shown up with a zs loop test with all protective conductors connected because of parallel paths... Where's my bad practice?
cheers
s
i thgink he meant isolating the installation by the main switch in the CU , so as to be able to disconnect main earth to measure Ze.HOW do you Issolate the supply fully? If its by removing DNO fuse then you are acting Illegaly and by recording this on cert you are admitting your guilt
.................Found this on a large testing companies website:
'Where the mains supply is connected, as will be the case for periodic testing, Perhaps 'will' should be replaced with 'may'.....the protective and equipotential conductors must not be disconnected because if a fault occurs these conductors may rise to a high potential above earth. In this case, an earth-fault loop tester can be used to verify the integrity of the protective system.'
So wrong, I wonder how many wrongly measured Ze readings they've reported (parallel paths). I emailed them suggesting they might consider turning of the main isolator to reduce the risk of the conductors rising to 'a high potential above earth' before disconnecting the main earth for a real Ze test..
Big company as well..
Ride em cowboy!..rather harsh....I dont really think where an install cannot reasonably be isolated for testing a Ze inludiing parallel paths is a cowboy practice...more of an operational necessity on occasion.
I didnt paste the whole page but this was part of a description for general practice in periodic inspection and testing. My point way back then was good practice would be to isolate the installation in the first instance. The cowboy thing was more in jest really, I'm sure they're a good company. Discussion moved on a bit to how satisfactory using a loop test for Zs would be. Although Ze can be arrived at by enquiry supposing there was say a problem with the DNO's strap on a TN-S which a Zs may not p/u because of parallel paths/ and so on...................
Yeah right! The regs do say 'by enquiry'. Ever tried to get a Ze spec in writing out of a supplier? And what if you suspect a problem with say a suppliers TN-S strap clamp (which I did just recently) they will ask you what the Ze is before they'll come out!
(When did 2391 come into this?)I think having just achieved the C&G2391 is just the beginning of the journey.
Ze, by inquiry is already available to you since the DNO will quote their maximum standard value. In fact they probably won't even bother to reply to you, because you should know this. However, the Ze will rarely be the maximum quoted value. and would be better measured.
Now smaller installations where complete isolation is possible then a Ze can be performed by disconnecting the earthing conductor from the MET. But anything larger, where total isolation is inconvenient or impossible then you must not disconnect any of the main protective conductors.
A Zs close to, or at, the main intake is perfectly acceptable method of verifying that there is a protective system in place and to verify that the TNS sheath is still providing a reasonable result