What are the differences between the EICR & EIC.
The letter R
What are the differences between the EICR & EIC.
The letter R
Do you not know which circumstances to use either report?
If you do not...you should not be testing
Post resurrection! :egypt:
Mainly correct if briefly covered.
A couple of points in red/orange
4) Check the main earthing conductors and main bonding conductors are continuous to Gas/Water
5) Continuity of protective and bonding conductors (R1 + R2) This is not R1+R2 and is the same as 4.
This is the one
5) Continuity of radial circuits circuit protective conductors (R1+R2)
Maximum at furthest point
6) Continuity of ring final circuit conductors
· r1 rn r2
· cross connect L1,N2, and cross connect L2 and N1, You can measure between them at this point this will give you the value you expect on all other sockets which should be equal to (r1+rn)/4
readings at each socket should be ¼ of r1+rn.
· Repeat above with L1, E2 and L2, E1 (highest reading recorded as R1+R2)
7) Insulation Resistance
Test at 500v dc neutral & line
Test at 500v dc line - cpc
Test at 500v dc neutral to cpc
Toggle switches on 2 way lighting and test again, not required for Neutral to cpc
remember all the tests for the RCD
Idn at 0.5, 1, 5 (if 30mA) at both +ve and -Ve half cycles
Test button works
Post resurrection! :egypt:
Mainly correct if briefly covered.
A couple of points in red/orange
4) Check the main earthing conductors and main bonding conductors are continuous to Gas/Water
5) Continuity of protective and bonding conductors (R1 + R2) This is not R1+R2 and is the same as 4.
This is the one
5) Continuity of radial circuits circuit protective conductors (R1+R2)
Maximum at furthest point
6) Continuity of ring final circuit conductors
· r1 rn r2
· cross connect L1,N2, and cross connect L2 and N1, You can measure between them at this point this will give you the value you expect on all other sockets which should be equal to (r1+rn)/4
readings at each socket should be ¼ of r1+rn.
· Repeat above with L1, E2 and L2, E1 (highest reading recorded as R1+R2)
7) Insulation Resistance
Test at 500v dc neutral & line
Test at 500v dc line - cpc
Test at 500v dc neutral to cpc
Toggle switches on 2 way lighting and test again, not required for Neutral to cpc
remember all the tests for the RCD
Idn at 0.5, 1, 5 (if 30mA) at both +ve and -Ve half cycles
Test button works