Cheers Sintra. That's a handy additional piece of info for determining ages of installations.
Discuss Basic Testing Procedures in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The actual supply is not switched off, the installation past the main breaker is switched off granted but not the supply. Anyone just about to take the 2391 practical may be confused as books including GN3 and OSG use the CRIPLER method and this is the way i've been taught to test within my 2391 course;
Dead tests:
Continuity of circuit protective conductors
Ring final circuit conductor continuity
Insulation resistance testing
Polarity
Live Tests:
Loop impedance test external (Ze)
Earth fault loop impedances (Zs)
RCD testing
Except that you don't have to follow any particular order in the 2391, as it's a PIR that you are completing, not an Initial Verification.
You can basically test in the order that suits you best.
Hi Almac, Ive read elswhere that you need the 2391 to prove you are competent to carry out these tests, unlike PAT testing where it was argued you did not the C&G to carry out PAT.Can these procedures be carried out by non electricians... I have my city and guilds pat testing and an HNC in electronics wondering if that makes me competent?