That's the problem with the NICEIC, which owns the ESC, they think that they make the Regulations.
In the ESC best practice guide, despite the fact that BS7671 requires all circuits of locations containing baths or showeres to have RCD protection.
There is no recommendation for a code where RCD protection is not provided.
Any work that is carried out, must meet the requirements of BS7671.
BS7671 requires that some socket-outlets and some cables concealed in walls should have RCD protection.
As such RCD protection must be provided (where required) only on the extended part of an existing circuit.
However BS7671 requires that all circuits of locations containing baths or showers be RCD protected.
According to Appendix 15, circuits start (and in the case of RFCs finish) at a DB.
As such the only way to comply with BS7671 when extending an existing circuit of a location containg a bath or shower, is to provide RCD protection for the circuit at the DB.