Called to quote for installing some IP rated down lights in a bathroom. Told guy he needed an RCD for altering light etc and he wasnt pleased. Some old un-named mcb's in his C.U so i told him either a seperate 1 way c.u would do it or a new C.U all together to bring it upto date. Nope didnt want it :( Why do people think its just put that there and off you go..... Grrrr

Anyways i was thinking, could a RCD Spur be fitted outside the bathroom (above door etc) to feed the new lights in the bathroom, would this do?
 
people think that we take them for rides and that gear costs us 20p for a job load..!! Walk away from it,

RCD spur = ÂŁ25
cheap RCBO = ÂŁ13 with ÂŁ2.00 enclosure plus cable... probably cost same price, what suggests he will not want to pay for the RCD spur either...!

its a notify job as well...! let some cowboy do what he wants and chase bigger fish mate!!
 
Last edited by a moderator:
people think that we take them for rides and that gear costs us 20p for a job load..!! Walk away from it,

RCD spur = ÂŁ25
cheap RCBO = ÂŁ13 with ÂŁ2.00 enclosure plus cable... probably cost same price, what suggests he will not want to pay for the RCD spur either...!

its a notify job as well...! let some cowboy do what he wants and chase bigger fish mate!!

Would you need rcd on lv downlights
 
regs say RCD in bathroom ( zoned areas )

Regulation 701.411.3.3 now requires that additional protection shall be provided for all circuits of the location by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1. This is a significant change. Previously (601-09-02), only
fixed current using equipment (other than electric showers) located in zone 1 required 30mA RCD protection and current using equipment (other than fixed current using equipment – such as a washing machine, if suitable for use in a bathroom, connected through a fused connection unit) in zone 3 required 30mA RCD protection. Regulation 701.411.3.3 means that all circuits, including lighting, electric showers, heated towel rails, etc., will require RCD protection, not exceeding 30 mA.
 
Last edited by a moderator:
regs say RCD in bathroom ( zoned areas )

Regulation 701.411.3.3 now requires that additional protection shall be provided for all circuits of the location by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1. This is a significant change. Previously (601-09-02), only
fixed current using equipment (other than electric showers) located in zone 1 required 30mA RCD protection and current using equipment (other than fixed current using equipment – such as a washing machine, if suitable for use in a bathroom, connected through a fused connection unit) in zone 3 required 30mA RCD protection. Regulation 701.411.3.3 means that all circuits, including lighting, electric showers, heated towel rails, etc., will require RCD protection, not exceeding 30 mA.


All parts of the location not just the zones.
 
So id be ok just to spur the new lights and leave the rest of the light circuit as is?

Still would test all the light circuit out etc but only my work in bathroom would be rcd from the spur and comply ?

ta
 
Not so, the feed from the consumer unit to your lights in the bathroom will all so require RCD protection, if they are less than 50 mm buried into the fabric of the building.
Assuming you have all so confirmed bonding ECT.
Regards KJ

 
Not so, the feed from the consumer unit to your lights in the bathroom will all so require RCD protection, if they are less than 50 mm buried into the fabric of the building.
Assuming you have all so confirmed bonding ECT.
Regards KJ

They are existing and not new keith. Only thing i will be changing is the bathroom light to 4 down lights.
 
Hi there, You have to conform to, to days regs if you are installing any new equipment eg bathroom lights, you have to bring the circuit you are working on and the bonding at the Origen up to today’s standards.
Regards KJ

 
Hi there, When you alter an existing circuit, you have to confirm the circuit can supply the addition load, and subsequent fault currents, there for you have to test the hole circuit, and confirm it complies to current regs,
Regards KJ
 

Reply to Bathroom lights RCD etc in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
145
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
944
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
490
  • Question
ok cheers for the help lads
Replies
7
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top