Hi all,
I'm refitting my bathroom in my first floor flat (top floor) built around 1989. It has 2 CUs, one for night storage and one for 24h electrics, they are of the 1980's era Crabtree, the label on the side says BS5486ART 13 CM16.
The hot and cold are run in plastic from the Immersion heater located outside the bathroom.
The mains water is supplied to the flat in plastic and then copper to the kitchen sink and toilet, this is "bonded" to the CU earth terminal.
Items with potential in the room :
The toilet has a short piece of copper pipe in the Outside Zone to the cistern.
There is a fan isolation switch in the Outside Zone (the fan unit is in the loft).
There is a shaver socket in the Outside Zone (isolation transformer type).
The ceiling is 2.45m high and therefore in the Outside Zone I believe.
I would like to fit fire rated IP65 downlights to the existing lighting circuit (which also has the fan and shaver socket on it).
So in short, there will be nothing with any potential in Zones 0,1 or 2. and there will be no new circuits.
Am I right in thinking that changing a central light to 4 downlights is not classed as a new circuit?.
I know a RCD is desirable but is it strictly necessary in this instance?
The flat will need to pass a EICR but I realy don't need the expense of changing the CUs as I'm on a budget.
Cheers,
John
I'm refitting my bathroom in my first floor flat (top floor) built around 1989. It has 2 CUs, one for night storage and one for 24h electrics, they are of the 1980's era Crabtree, the label on the side says BS5486ART 13 CM16.
The hot and cold are run in plastic from the Immersion heater located outside the bathroom.
The mains water is supplied to the flat in plastic and then copper to the kitchen sink and toilet, this is "bonded" to the CU earth terminal.
Items with potential in the room :
The toilet has a short piece of copper pipe in the Outside Zone to the cistern.
There is a fan isolation switch in the Outside Zone (the fan unit is in the loft).
There is a shaver socket in the Outside Zone (isolation transformer type).
The ceiling is 2.45m high and therefore in the Outside Zone I believe.
I would like to fit fire rated IP65 downlights to the existing lighting circuit (which also has the fan and shaver socket on it).
So in short, there will be nothing with any potential in Zones 0,1 or 2. and there will be no new circuits.
Am I right in thinking that changing a central light to 4 downlights is not classed as a new circuit?.
I know a RCD is desirable but is it strictly necessary in this instance?
The flat will need to pass a EICR but I realy don't need the expense of changing the CUs as I'm on a budget.
Cheers,
John