Crosswire

If an installation is supplied by a two wire system (E.G. a TT system) , what are the benefits of using an earth electrode instead of simply joining earth to neutral at the supply head to create a TNCS system?

Surely using the supplier's neutral is a more effective return path for fault current than relying on the earth electrode and the solid mass of earth?

All replies welcome,

Cheers,
Crosswire.
 
All I can say on the subject of bread rolls is that I've been enjoying a bacon butty in the site canteen of a morning recently. But what I can say about using the neutral as the fault current return path is that one important fact has not been explicitly stated in answer to the OP's question regarding the dangers of a neutral loss in TN-C-S.

If you are relying on the neutral connection all the way back to the transformer as your fault path and it fails, not only is the fault protection lost but all current returning from loads downstream of the fault will be diverted via MEBs and casual earth connections, which might or might not provide a suitably low resistance path to stop everything being lifted to a dangerous voltage WRT true earth. For instance, if the distribution cable N fails in an area with plastic gas and water services, every piece of exposed metalwork in everyone's installation might be raised 230V from earth as soon as anyone switches on a load, even in the absence of a fault within the installations. In other words, the earthing system becomes a source of danger, instead of reducing it.

Hence the need to ensure highest possible integrity of the PEN, and hence PME. Random local N-E links don't guarantee the necessary integrity upstream.
 
Far too much scaremongering goes on about DNO PME supplies. If you listen to some on here, death and/or destruction is waiting for you just round the corner if you happen to have a TNC-S/PME supply!!

You are far more likely to have a DNO TNC-S supply, if you're house/flat is older and has been converted from a deteriorating TN-S supply. If you live in a relatively modern house/flat then the chances are that it will be a full DNO PME system where all the relevant cable joints have been N-E grounded. The same will go for DNO overhead supplies, that have been PME'd, it will be a full bona fide PME system. It is also easy to confirm if overhead system has been PME'd by checking the poles for the down lead N-E link to the earth rods/electrodes, (every 3rd or 4th pole)...

Oh and i also take with a good pinch of salt, those that claim they have seen a lost neutral on PME systems on several occasions, ....it's rare, it's very rare to completely lose a neutral connection!!
 
Far too much scaremongering goes on about DNO PME supplies. If you listen to some on here, death and/or destruction is waiting for you just round the corner if you happen to have a TNC-S/PME supply!!

You are far more likely to have a DNO TNC-S supply, if you're house/flat is older and has been converted from a deteriorating TN-S supply. If you live in a relatively modern house/flat then the chances are that it will be a full DNO PME system where all the relevant cable joints have been N-E grounded. The same will go for DNO overhead supplies, that have been PME'd, it will be a full bona fide PME system. It is also easy to confirm if overhead system has been PME'd by checking the poles for the down lead N-E link to the earth rods/electrodes, (every 3rd or 4th pole)...

Oh and i also take with a good pinch of salt, those that claim they have seen a lost neutral on PME systems on several occasions, ....it's rare, it's very rare to completely lose a neutral connection!!

The 2 I have seen were not completely open circuit, but high-impedance. This was on a fairly modern (1970s) street. Keep denying it happens by all means, but next time it happens to me I'll get you to touch the metal clad light switch in my garage and see what you think :) Daz
 
The 2 I have seen were not completely open circuit, but high-impedance. This was on a fairly modern (1970s) street. Keep denying it happens by all means, but next time it happens to me I'll get you to touch the metal clad light switch in my garage and see what you think :) Daz


Eh, .... A high impedance fault is hardly a lost neutral is it!! lol!!

I am not denying that it can and does happen, but lost neutrals especially on a full PME systems are as almost as rare as hen's teeth!!

Think about it, how can a modern industrialised western nation run an electrical network system that is known to drop neutrals on a regular and ongoing basis, putting both life and property at risk??

Just imagine the costs involved to the electric companies, with the multitude of legal cases!!!
 
It may not be a lost neutral, but they were poor joints on neutrals on a modern PME system. These joints would only get worse and worse over time and become a lost neutral at some point surely.
 
If the 'high impedance' multiplied by the load current is above 50V, then for safety purposes it's a lost neutral. A shower running into a 2Ω PEN could cause some nasty shocks even when the EB is up to scratch for PME.

Open or high-resistance connections can occur in any conductor. They are rare in DNO works but in the case of TN-C and TN-C-S PENs they cause a specific hazard that doesn't exist in other supply configurations, namely the protective conductors and ECPs of connected installations can be elevated to hazardous voltages absent any other faults.

I don't think anyone is saying PME is deficient for this reason, only that it's no good to go around making random N-E connections and assuming that a TN-S neutral would automatically be a better place than a rod to connect the earthing conductor.
 
I don't think anyone is saying PME is deficient for this reason, only that it's no good to go around making random N-E connections and assuming that a TN-S neutral would automatically be a better place than a rod to connect the earthing conductor.

Now that i CAN agree with!!

High impedance faults don't just magically or instantly just happen by the way, they manifest themselves over a period of time. Again highly unlikely that a high impedance neutral fault wouldn't have made itself known long before it got to the point of being dangerous/hazardous... But again, yes it can and does happen, and yet again, it's going to be a rare, rare, rare occurrence.....
 
Now that i CAN agree with!!

High impedance faults don't just magically or instantly just happen by the way, they manifest themselves over a period of time. Again highly unlikely that a high impedance neutral fault wouldn't have made itself known long before it got to the point of being dangerous/hazardous... But again, yes it can and does happen, and yet again, it's going to be a rare, rare, rare occurrence.....

So it seems that the table from wikipedia that ranked the risk of neutral loss on a TNCS earthing system as hgh, is misleading?

This is why I sought the opinion of time served sparks, so as to explode myths and bring clarification on earthing systems. Cheers!
 
Never seen one occur out in the field in all my years of being a spark, but do understand the potential for a fault.

On another note.......our on site 11kv transformer was changed 3 years ago and the DNO went to a great deal of effort to install an earth nest along with 4x rods buried 3 rods each deep to get a ze of 0.08 ohms.

The DNO does take it's earthing seriously, sometimes
 

Reply to Benefits of a TT system? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
668
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top