If an installation is supplied by a two wire system (E.G. a TT system) , what are the benefits of using an earth electrode instead of simply joining earth to neutral at the supply head to create a TNCS system?

Surely using the supplier's neutral is a more effective return path for fault current than relying on the earth electrode and the solid mass of earth?

All replies welcome,

Cheers,
Crosswire.
 
In a TNCS the fault path uses the neutral (yes I know you know that) so if the neutral breaks and there's a fault inside the installation then you could have every metal part inside it live. In a TT you still have the fault path through the general mass of earth.
TTs are not just used in rural/remote locations, we live near a main road into a fairly busy town and we're on a TT (Ra > 1 ohm)

and that's the reason you can't use TNC-S for caravans ( metal bodied). someone correct me if i'm wrong.
 
In a TNCS the fault path uses the neutral (yes I know you know that) so if the neutral breaks and there's a fault inside the installation then you could have every metal part inside it live. In a TT you still have the fault path through the general mass of earth.
TTs are not just used in rural/remote locations, we live near a main road into a fairly busy town and we're on a TT (Ra > 1 ohm)

I see. So would it be a good idea to use a TNCS system ( which is good if it is working correctly), backed up by an earth electrode to provide an alternative path, should the neutral fail?
 
I see. So would it be a good idea to use a TNCS system ( which is good if it is working correctly), backed up by an earth electrode to provide an alternative path, should the neutral fail?
Although I'm assured by my learned friends here that it does happen I've not seen a failed neutral on a TN in my 34 years in the trade. I've seen whole cables fail but not just the N.
Some countries do exactly what you're talking about so maybe it would be a good idea if it were adopted here. Would I do it? Probably not
 
Crosswire that is effectively what IS done, the bonds to the gas and water, although no one will admit it, act as back up TT rods (obviously only if metal).

Almost every time I have found a half decent TT reading, it is due to the parallel paths to these services, not the electrode itself.
 
Crosswire that is effectively what IS done, the bonds to the gas and water, although no one will admit it, act as back up TT rods (obviously only if metal).

Almost every time I have found a half decent TT reading, it is due to the parallel paths to these services, not the electrode itself.
Fancy a cuppa at wor hoose? Bring ya tester :)
 
Although I'm assured by my learned friends here that it does happen I've not seen a failed neutral on a TN in my 34 years in the trade. I've seen whole cables fail but not just the N.
Some countries do exactly what you're talking about so maybe it would be a good idea if it were adopted here. Would I do it? Probably not

Maybe a burnout at the supply head caused by a high resistance connection on the neutral might do this, but I also have never seen it personally.

I also have never driven earth electrodes to back up the TNCS earthing, I always relied on the supplier's earth ( which they are apparantly "not obliged to provide") once the Ze has been confirmed.

Anyhow, all good food for thought, as I find this subject fascinating. :)
 
Maybe a burnout at the supply head caused by a high resistance connection on the neutral might do this, but I also have never seen it personally.

I also have never driven earth electrodes to back up the TNCS earthing, I always relied on the supplier's earth ( which they are apparantly "not obliged to provide") once the Ze has been confirmed.

Anyhow, all good food for thought, as I find this subject fascinating. :)
Not obliged to provide but are obliged to maintain if they do
 
had a call-out the other week. elderly disabled gent. i'd done him a CU upgrade some months ago. his daughter phoned me---no power.

thinking possible RCD trip, called round. at the incomer found L-N 0V. L-E 245V, N-E 180V. called DNO who called @ 6.15pm. they confirmed it was a supply fault. after digging up the road, they found a faile N connection where he was tapped off the underground feeder.
 

Reply to Benefits of a TT system? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
668
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top