The reason I would still go for a delay-RCD as a main switch (not as a separate enclosure) is to avoid a single point of failure in the RCD/RCBO electronics.
As mentioned above, an all-RCBO board does not need any up-front RCD to meet disconnection times, so long as the RCD action works. But folk never test them, and they are an order of magnitude more complex than the thermal/magnetic trip of a MCB (or equivalent aspect of a RCBO) that would be the back-up in a TN system (but is not going to trip in a TT system).
So if there is pressure on the budget then a simple incoming DP isolation switch is fine with an all RCBO board (or similar) as it is fully compliant, but to me that is not the best setup.