Octopus
Got called out yesterday, wife's friend has no power (since Thursday night) and their 2nd BG call for Saturday had been cancelled and re-scheduled for Sunday
Family of 5, no power
So I turn up to find they have 1 extension lead running the fridge freezer from their neighbour .............
So a quick visual :
3 year old metal clad board with RCD main switch
3 circuits (sockets, central heating and lights)
A quick set of tests
dead short on N-E on the lighting circuit, so with the customers agreement I disconnected the lighting and left them with sockets and central heating.
What I want to know is why the BG muppet who attended site on Thursday couldn't do what I did?
And why the loft conversion company thought it was acceptable to extend the existing socket and lights to incorporate the loft conversion AND think a RCD main switch was a good idea ......