Got called out yesterday, wife's friend has no power (since Thursday night) and their 2nd BG call for Saturday had been cancelled and re-scheduled for Sunday

Family of 5, no power

So I turn up to find they have 1 extension lead running the fridge freezer from their neighbour .............

So a quick visual :

3 year old metal clad board with RCD main switch
3 circuits (sockets, central heating and lights)

A quick set of tests

dead short on N-E on the lighting circuit, so with the customers agreement I disconnected the lighting and left them with sockets and central heating.

What I want to know is why the BG muppet who attended site on Thursday couldn't do what I did?

And why the loft conversion company thought it was acceptable to extend the existing socket and lights to incorporate the loft conversion AND think a RCD main switch was a good idea ......

I despair
 
Most of the BG electricians were directly employed (this was in 2005), I worked in the west Midlands, another guy on my patch was rubbish at his job.

I was only there for 2 months as BG were cowboys, and left.
 
I have seen many electrical companies going into mechanical/plumbing and visa versa because they think it is a good idea to provide M &E and it always folds the company or the end up ditching the idea as it nearly puts the company under.
 
I have seen many electrical companies going into mechanical/plumbing and visa versa because they think it is a good idea to provide M &E and it always folds the company or the end up ditching the idea as it nearly puts the company under.
This is very much customer driven, in my opinion, many facilities managers want a one stop shop as they can't be arsed having to ring multiple companies to resolve issues.
 
BG's sales strategy is shameful and fraudulent,in my opinion....it's commercial department,more so.

It puts me in mind of a certain high-street bank,who acted in a similar fashion,also saving the worst of it's behaviour,for their commercial customers.

The bank in question,is facing legal problems and payouts,right now,regarding this past policy.....and policy,it was.

I firmly believe,this will be BG's destiny,and as with the above mentioned bank,they will remain in place,to annoy us :rolleyes:
 

Reply to BG Incompetence strikes again in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
590
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
771
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top