big problem | Page 2 | on ElectriciansForums
Discuss big problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A Test with clamp on amp meter with all the lights running will soon give you the full load,but if the lamps are 70watt the load will be well under 10amps in which case you zs of 3.64 will be fine with a 10amp type B or you could go to a 6amp type C
Test with clamp meter and assess load in reference to the design current for the circuit.
Measure R1+R2.
Measure Zs at distribution board.
Measure Zs at circuit.
Look for any abnormal results across the above ^.
60898 Type B 6Amp or 10Amp will be fine IMO.
Reply to big problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...