Bizarre dead short between Neutral and Earth | on ElectriciansForums

Discuss Bizarre dead short between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net

1

1shortcircuit

Firstly, please let me explain the fault on the circuit HAS been rectified. This was achieved by splitting the offending circuit (kitchen ring) into two radials and putting each leg on their own 16A mcb on the same RCD.

Attended a property to do some remedial works on the kitchen ring, New dual RCD protected board already installed and just there to put rubber grommets into back boxes. Such a joy:tongue3:

Anyway as I always test circuits before working on them I found a dead short between Neutral and Earth but RCD holds?

RCD tests came back well within specified tripping times on x1 and x5 tests but RCD failed to recognise this dead short?

Anyone have any suggestions as to why this RCD will test fine but not do it's job as intended?

All testing was done with circuit completely removed from Consumer Unit. Faulty leg found between two sockets so removed and as said made ring into two radials, each on their own mcb (same RCD). Comment sticker left on consumer unit explaining circuits 2 & 3 both energise kicthen.

Kind Regards

1SC
 
and then look for the nail.

Well it seems the kitchen cabinets MAY have been screwed to the wall and from what I can tell the cabling has not followed safe zones so it could have been a screw I guess??? Could be here all day guessing which is why I just cut out the faulty link and created two radials

Also take a link of cable and short neutral and earth at the CU just to confirm then say the cooker circuit is on the same RCD then get your r1 r2 test plug at at the cooker outlet short out N-E

I was wondering this myself, Just to prove that in the event there is a fault the RCD does actually do what it's supposed to do.

I did contact Elecsa, who I must add have been excellent on the two occasions that I have needed to contact them and even they said it doesn't make sense.

Thanks for everyone's input:thumbsup
 
Ah ha i bet its a nail like tel has said had one simular all readings were ok RCD tripping time hunky dory , with the circuits operating all fine then RCD would trip for no reason drove me mad trying to find it new RCD's etc as you do tested circuit all clear then the RCD would trip , located the fault to a capping nail that was straight through the cable it was intermittantly shorting and tripping the RCD pig to find so it could well be an intermittant short
 

Reply to Bizarre dead short between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
383
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top