Firstly, please let me explain the fault on the circuit HAS been rectified. This was achieved by splitting the offending circuit (kitchen ring) into two radials and putting each leg on their own 16A mcb on the same RCD.
Attended a property to do some remedial works on the kitchen ring, New dual RCD protected board already installed and just there to put rubber grommets into back boxes. Such a joy:tongue3:
Anyway as I always test circuits before working on them I found a dead short between Neutral and Earth but RCD holds?
RCD tests came back well within specified tripping times on x1 and x5 tests but RCD failed to recognise this dead short?
Anyone have any suggestions as to why this RCD will test fine but not do it's job as intended?
All testing was done with circuit completely removed from Consumer Unit. Faulty leg found between two sockets so removed and as said made ring into two radials, each on their own mcb (same RCD). Comment sticker left on consumer unit explaining circuits 2 & 3 both energise kicthen.
Kind Regards
1SC
Attended a property to do some remedial works on the kitchen ring, New dual RCD protected board already installed and just there to put rubber grommets into back boxes. Such a joy:tongue3:
Anyway as I always test circuits before working on them I found a dead short between Neutral and Earth but RCD holds?
RCD tests came back well within specified tripping times on x1 and x5 tests but RCD failed to recognise this dead short?
Anyone have any suggestions as to why this RCD will test fine but not do it's job as intended?
All testing was done with circuit completely removed from Consumer Unit. Faulty leg found between two sockets so removed and as said made ring into two radials, each on their own mcb (same RCD). Comment sticker left on consumer unit explaining circuits 2 & 3 both energise kicthen.